    Default Adding 2 more PIR to a zone Bosch Gen 2?

    Hi All

    I'm a little stuck, searched the big wide web and cant find anything on the way this PIR is wired. I want to add two more PIR's to this PIR, so 3 in one zone.
    Where does the resistor go?
    Do I remove it and fit it into the last PIR?
    Do I add the same resistor to each PIR? where do I connect the other wires, I know the + - that's the easy bit.

    Thanks in Advance



Look Here ->
  • #2
    Senior Member
    Join Date
    Jan 2009
    Age
    45
    Posts
    555
    Thanks
    2
    Thanked 82 Times in 64 Posts
    Rep Power
    236
    Reputation
    1564

    Default

    Don't do it, if there is ever an alarm how would you know what PIR caused it?

  • #3
    Junior Member
    Join Date
    Feb 2017
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    Thanks Xr5adam, the one i want to come off is in the garage, I have just built a shed and adding the two extra PIR's in there so not too bothered. I would have gone straight to the panel but its full.

  • #4
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    911
    Thanks
    157
    Thanked 147 Times in 134 Posts
    Rep Power
    277
    Reputation
    2429

    Default

    Run it to the panel any way, so if you ever upgrade you can then put them on own zones.
    It needs to be connected in series. 1 zone 1 resistor 3 devices.