Solution 862 alarm system
Hi guys I am new to this site and desperate for some help please.
We have a Solution 862 alarm system and have recently replaced the rechargeable battery and fuses x 3. The control panel shows operators programming mode ie house with man inside/man walking away, power ON, codes 3 and 7. Please can someone help me to reset it? Thank you Suse :-)
-
Junior Member
- Rep Power
- 201
- Reputation
- 56
Set time and date and then arm/disarm
Junior Member
- Rep Power
- 0
- Reputation
- 30
Sounds like the unit may possibly have reset to factory default - do your previous master/installer codes still work or have they reset to defaults (2580/1234)?
I think the 3 & 7 showing mean that these zones aren't sealed. Do you know if you were using these zones previuosly and what they were assigned to (by default zone 7 is "24 Hour Fire")? If you were not using previously, then you can update zone coding to say they are not in use (and the numbers should clear from the display). Change zone type to value 15 for "zone not used". For the 880, zone 3 zone type is at location 281 and zone 7 zone type is at 309 - but this you'd better check doco for the 862.