    Default Bosch 3000 - PIR Setup Issue

    Guys,

    I am replacing an old solution 8 panel and PIRs and have an issue that I just cannot work out.

    I have tried wiring these 3 in multiple ways and I am still getting a trigger note on the screen.

    The unit detects movement but doesn't trigger the panel to alarm.

    The current setup is as follows in the photos

    I have also tried having the resistor just across the NC / NC and leaving the T / T empty.

    I haven't even goto the connectix 3G yet so that will be interesting to setup im sure....










Look Here ->
  • #2
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    907
    Thanks
    156
    Thanked 146 Times in 133 Posts
    Rep Power
    276
    Reputation
    2409

    Default

    What zones are the pirs wired to in the panel.
    I think they have the wrong value resistors in them.
    On the 3000 the first 8 zones are 3k3 resistors and when zone doubled 9-16 are 6k8.
    The picture shows 6k8 resistors in pirs.

  • #3
    Junior Member
    Join Date
    Feb 2008
    Posts
    46
    Thanks
    5
    Thanked 0 Times in 0 Posts
    Rep Power
    198
    Reputation
    10

    Default

    Thanks Secure.... What a dope yes I didn't realise I had both types supplied with the panel and was using the 6k8.

    I switched over to the 3k3 and put that across the N/C and left the tamper ports empty but I am getting same on the panel.

    Do I need to have something across the tamper ports also?

  • #4
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    907
    Thanks
    156
    Thanked 146 Times in 133 Posts
    Rep Power
    276
    Reputation
    2409

    Default

    how your picture is, is ok, just needed the right resistor.

  • The Following User Says Thank You to secure For This Useful Post:

    xapi (11-02-18)

  • #5
    Banned
    Join Date
    Nov 2013
    Posts
    29
    Thanks
    1
    Thanked 4 Times in 4 Posts
    Rep Power
    0
    Reputation
    70

    Default

    You need to make sure with these new Blueline PIRs that you have at least 8mm of copper (doubled over) in the screw terminals. I have found anything less can sometimes give you this problem. Good luck.