    Default IEC Female plug and lead using 1.0mm sq cable. Is it too small for 800W Max

    I'm very surprise that leads today for UPS that use a IEC Female plug from your power point to the UPS use only a 1.0MM lead and this it rated at 10 amps. you would think they should be at least 1.5MMsq? Can someone tell me a typical extension lead around 20M rated at 10 Amps what size cable they uses?.
    Yes I need a lead a 0.5M longer and I want to buy the IEC plug itself and make my own lead using 1.5MM cable, I have a roll of 1.5MM cable, I have the 3 pin plug for the power Point but its not easy to buy The Rewireable IEC Female Plug. Ebay does not have them not unless you get them from the UK and it seems RS is the only other mob that stocks them.
    Any though where you can get them locally or even a Electrical wholesaler.
    Thanks
    Not responsible for any post written after the 28/10/2014. My pet hate, Corrupt Politicians, Corrupt Legal System + a legal system Australia wide that does not allow you to sue a Solicitor or Barrister for Professional Negligence (as Stated by the Law Society and prominent Lawyers) and Corrupt Cops. Not necessarily in this order. Please Note Lawyers are PROTECTED SPECIES IN THIS COUNTRY, PROTECTED FROM THEIR F..K UPS



Look Here ->
  • #2
    Senior Member
    Reschs's Avatar
    Join Date
    Aug 2010
    Location
    Outside a few schooners
    Posts
    2,464
    Thanks
    487
    Thanked 1,352 Times in 692 Posts
    Rep Power
    530
    Reputation
    17338

    Default

    Altronics or Jaycar both sell them.
    Wagner Electronic Services ( WES) in Ashfield, Sydney.

  • #3
    Senior Member
    Reschs's Avatar
    Join Date
    Aug 2010
    Location
    Outside a few schooners
    Posts
    2,464
    Thanks
    487
    Thanked 1,352 Times in 692 Posts
    Rep Power
    530
    Reputation
    17338

    Default

    You could just buy a longer premade IEC Lead. They do come in various lengths.
    800 Watt is under 4 Amps, so a 10 Amp Lead is more than enough.

  • #4
    Premium Member
    Skepticist's Avatar
    Join Date
    Apr 2009
    Posts
    972
    Thanks
    373
    Thanked 497 Times in 415 Posts
    Rep Power
    336
    Reputation
    9320

    Default

    10A is the rated max current from a standard GPO IE 2.4kW.

  • #5
    Premium Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    3,042
    Thanks
    775
    Thanked 734 Times in 419 Posts
    Rep Power
    423
    Reputation
    12185

    Default

    Quote Originally Posted by Reschs View Post
    You could just buy a longer premade IEC Lead. They do come in various lengths.
    800 Watt is under 4 Amps, so a 10 Amp Lead is more than enough.
    Yes I look at a longer lead from ebay and I can cut off the 3 pin plug and shorten the lead and re plug it but thinking 1.0mm. Although its rated for 10 amps I always though that 1.5MM SQ is the smalless for 10AMP not 1.0MMSq
    Not responsible for any post written after the 28/10/2014. My pet hate, Corrupt Politicians, Corrupt Legal System + a legal system Australia wide that does not allow you to sue a Solicitor or Barrister for Professional Negligence (as Stated by the Law Society and prominent Lawyers) and Corrupt Cops. Not necessarily in this order. Please Note Lawyers are PROTECTED SPECIES IN THIS COUNTRY, PROTECTED FROM THEIR F..K UPS

  • #6
    Premium Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    3,042
    Thanks
    775
    Thanked 734 Times in 419 Posts
    Rep Power
    423
    Reputation
    12185

    Default

    Quote Originally Posted by Skepticist View Post
    10A is the rated max current from a standard GPO IE 2.4kW.
    i'm talking about the IEC Plug that they Call KETTLE lead.. Me thinks that 1.0MM is too small
    Not responsible for any post written after the 28/10/2014. My pet hate, Corrupt Politicians, Corrupt Legal System + a legal system Australia wide that does not allow you to sue a Solicitor or Barrister for Professional Negligence (as Stated by the Law Society and prominent Lawyers) and Corrupt Cops. Not necessarily in this order. Please Note Lawyers are PROTECTED SPECIES IN THIS COUNTRY, PROTECTED FROM THEIR F..K UPS

  • #7
    Premium Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    3,042
    Thanks
    775
    Thanked 734 Times in 419 Posts
    Rep Power
    423
    Reputation
    12185

    Default

    Quote Originally Posted by Reschs View Post
    Altronics or Jaycar both sell them.
    Wagner Electronic Services ( WES) in Ashfield, Sydney.
    I look at Jaycar on the net and they sell the IEC Male plug not the female one. Could have possible missed it.
    Not responsible for any post written after the 28/10/2014. My pet hate, Corrupt Politicians, Corrupt Legal System + a legal system Australia wide that does not allow you to sue a Solicitor or Barrister for Professional Negligence (as Stated by the Law Society and prominent Lawyers) and Corrupt Cops. Not necessarily in this order. Please Note Lawyers are PROTECTED SPECIES IN THIS COUNTRY, PROTECTED FROM THEIR F..K UPS

  • #8
    Administrator
    mtv's Avatar
    Join Date
    Apr 2008
    Posts
    17,273
    Thanks
    4,963
    Thanked 10,922 Times in 5,436 Posts
    Rep Power
    3764
    Reputation
    152970

    Default

    Quote Originally Posted by Mr 672A View Post
    I look at Jaycar on the net and they sell the IEC Male plug not the female one. Could have possible missed it.



  • The Following User Says Thank You to mtv For This Useful Post:

    Mr 672A (12-03-18)

  • #9
    Senior Member

    Join Date
    Feb 2008
    Location
    Mid North Coast NSW . Australia
    Age
    62
    Posts
    1,894
    Thanks
    1,103
    Thanked 352 Times in 238 Posts
    Rep Power
    294
    Reputation
    4957

    Default

    That's kinda odd...Jaycar are calling them male plug and female socket, Should be female plug and male socket

  • #10
    Administrator
    mtv's Avatar
    Join Date
    Apr 2008
    Posts
    17,273
    Thanks
    4,963
    Thanked 10,922 Times in 5,436 Posts
    Rep Power
    3764
    Reputation
    152970

    Default

    Quote Originally Posted by loopyloo View Post
    That's kinda odd...Jaycar are calling them male plug and female socket, Should be female plug and male socket
    Any connector with pins is usually referred to as a plug and any connector with receptacles is usually referred to as a socket.

  • The Following 2 Users Say Thank You to mtv For This Useful Post:

    loopyloo (13-03-18),Mr 672A (12-03-18)

  • #11
    Premium Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    3,042
    Thanks
    775
    Thanked 734 Times in 419 Posts
    Rep Power
    423
    Reputation
    12185

    Smile

    Quote Originally Posted by mtv View Post
    Any connector with pins is usually referred to as a plug and any connector with receptacles is usually referred to as a socket.
    Thank you my Friend you are always on the Ball. I searched the Jaycar Thick and thin and I only found the Male one not the Female one and I need at Female one. For me Its confusing even more after the stroke so what I do now If it has something long coming out its a MALE and it it has a HOLE its a Female. (we heard that Before).
    On the UPS they dont recommend using extension leads from the Power point to the Original supplied Input lead with the IEC plug on the end of it and since most all IEC leads are 1.0MM it think its no good (maybe I'm paranoid the lead needs to be 2.5M long )Sq I want to make the exact distance from the PP to the UPS from 1.5 MM Sq cable which is a little thicker on the outside. I also have a full roll of 2.5MM 3 core Extension cable but the outside diameter is a lot thicker and it would be a pain for the male three pin plug and the IEC female on the other end.
    I will ring Jaycar and trott over there today if they have in in stock.
    Not responsible for any post written after the 28/10/2014. My pet hate, Corrupt Politicians, Corrupt Legal System + a legal system Australia wide that does not allow you to sue a Solicitor or Barrister for Professional Negligence (as Stated by the Law Society and prominent Lawyers) and Corrupt Cops. Not necessarily in this order. Please Note Lawyers are PROTECTED SPECIES IN THIS COUNTRY, PROTECTED FROM THEIR F..K UPS

  • #12
    Premium Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    3,042
    Thanks
    775
    Thanked 734 Times in 419 Posts
    Rep Power
    423
    Reputation
    12185

    Default

    Done with a 1.5 Lead. All good, thanks All
    Not responsible for any post written after the 28/10/2014. My pet hate, Corrupt Politicians, Corrupt Legal System + a legal system Australia wide that does not allow you to sue a Solicitor or Barrister for Professional Negligence (as Stated by the Law Society and prominent Lawyers) and Corrupt Cops. Not necessarily in this order. Please Note Lawyers are PROTECTED SPECIES IN THIS COUNTRY, PROTECTED FROM THEIR F..K UPS

  • #13
    Premium Member
    Skepticist's Avatar
    Join Date
    Apr 2009
    Posts
    972
    Thanks
    373
    Thanked 497 Times in 415 Posts
    Rep Power
    336
    Reputation
    9320

    Default

    What I do when a custom length IEC power lead is required is get a cheap 10A extension lead that comes in 3, 5 or 10m lengths from the bargain store, lop off the standard in-line socket and fit the IEC plug. Quick and doesn't break the bank.