    Default strange powerpack problem

    g'day ppl

    i have a powerpoint i wired myself wired from house powerpoint to outside dunny only using 2 wires it goes into a floro light then out to powerpoint ,originally it was just for light but i then wanted to hook up a a wireless network & outside dunny was best position so i wired the powerpoint from the light...

    now for some odd reason when the wifi ap powerpack is plugged in with powerpoint switched off i'm getting a slight zap from the powerpack connector,

    its output is 5vDC 2.5 amp its a cheap switchmode powerpack from jaycar

    the original power pack for ap blew up over 12months ago..
    now the ap works fine but it only runs for about a week then i have to switch off then leave for few hours then turn it back on for another week..

    just wanting to know if its my shonky wireing or i need a better power pack &
    can someone tell me where i can get a decent one in melb.. btw the ap only needs 2amps ... thanks in advance.



Look Here ->
  • #2
    Junior Member kalboy's Avatar
    Join Date
    Jan 2008
    Location
    Kalgoorlie W.A
    Posts
    93
    Thanks
    9
    Thanked 2 Times in 2 Posts
    Rep Power
    202
    Reputation
    17

    Default

    wow....
    I guess your not a sparky or are you joking.
    You have a HOT neutral caused by your fluoro.
    what are you using for an earth, due you have a connection between the fluoro chasis and the toilet pipes. ?

  • #3
    Junior Member
    Join Date
    Jan 2008
    Location
    Melbourne
    Posts
    33
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    200
    Reputation
    11

    Default

    no joking & aint a sparky & no earth at all well ap is a external unit homemade in a alum case & it is earthed but floro aint earthed..

  • #4
    Senior Member
    mango's Avatar
    Join Date
    Jan 2008
    Location
    QLD
    Posts
    3,159
    Thanks
    25
    Thanked 1,048 Times in 533 Posts
    Rep Power
    454
    Reputation
    7506

    Default

    u might very well soon be CRISP kringle lol

  • #5
    Senior Member
    best4less's Avatar
    Join Date
    Jan 2008
    Location
    Australia
    Posts
    7,684
    Thanks
    3,487
    Thanked 2,207 Times in 1,132 Posts
    Rep Power
    758
    Reputation
    15165

    Default

    KRINGLE mate leave the plug pack in the house and just extend
    the wires from that to outside that will be defenetly your
    safest bet

    mango CRISP kringle lol LMFAO
    When you do things right, people won't be sure that you have done anything at all

  • #6
    Junior Member
    Join Date
    Jan 2008
    Location
    Melbourne
    Posts
    33
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    200
    Reputation
    11

    Default

    ok looks like the lack of earth is my problem.. right so i'll fix it today by rewiring with 3 core & that should fix the problem. i'll allso add a junction box so the powerpoint aint directly wired to light.. thanks for insight..

  • #7
    Senior Member BCNZ's Avatar
    Join Date
    Jan 2008
    Location
    In the back of a 50 kW AM broadcast transmitter
    Posts
    1,697
    Thanks
    235
    Thanked 292 Times in 190 Posts
    Rep Power
    305
    Reputation
    2546

    Default

    People who are not sparkies and have little understanding of basic electrical principles scare me...

    The potential for someone to be plated or for a kid to come along and die from someone's bodgy installation is huge.

    No earths, connections twisted together, mains run using 300 ohm ribbon cable, transposed phase and neutral .. all just accidents waiting to happen.

    Problem is, I come across all these things and more in my day to day work.
    Why people take risks with electricity is beyond me.

    As Kevin Bloody Wilson says "We're the only tradespeople that work with something that ya can't see!"

  • #8
    Junior Member TZB's Avatar
    Join Date
    Jan 2008
    Location
    Canberra
    Posts
    246
    Thanks
    66
    Thanked 39 Times in 27 Posts
    Rep Power
    218
    Reputation
    585

    Default

    I thought Kevin Bloody Wilson was a teacher not a sparky

  • #9
    Senior Member BCNZ's Avatar
    Join Date
    Jan 2008
    Location
    In the back of a 50 kW AM broadcast transmitter
    Posts
    1,697
    Thanks
    235
    Thanked 292 Times in 190 Posts
    Rep Power
    305
    Reputation
    2546

    Default

    He worked as a sparky in the mines at Kalgoorlie some years before he was a comedian.

    I'm trying to work out what the guy in your avatar is doing before he gets the BSOD.

  • #10
    Senior Member
    Join Date
    Jan 2008
    Posts
    701
    Thanks
    13
    Thanked 51 Times in 40 Posts
    Rep Power
    226
    Reputation
    257

    Default

    un****inbeleiveable

  • #11
    Senior Member RHCP's Avatar
    Join Date
    Jan 2008
    Location
    Molesting a Cow
    Age
    38
    Posts
    740
    Thanks
    58
    Thanked 147 Times in 96 Posts
    Rep Power
    237
    Reputation
    728

    Default

    Quote Originally Posted by Studio1 View Post
    I'm trying to work out what the guy in your avatar is doing before he gets the BSOD.
    It's Data from Star Trek Next Gen! He's probably doing something awesome, like recalibrating the sensors to allow for plasma ion fluctuations

    Cheers, RHCP.
    Democracy: Three wolves and a sheep voting on what's for lunch.

  • #12
    Junior Member TZB's Avatar
    Join Date
    Jan 2008
    Location
    Canberra
    Posts
    246
    Thanks
    66
    Thanked 39 Times in 27 Posts
    Rep Power
    218
    Reputation
    585

    Default

    Right on RHCP, here's the full size image (I had to reduce it for my avatar).


  • #13
    Junior Member
    Join Date
    Jan 2008
    Location
    Melbourne
    Posts
    33
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    200
    Reputation
    11

    Default

    the light that I originally wired is of a type that has no earth. my minor mistake was later down the track wiring a powerpoint in & just not thinking that it would need to be earthed so its a minor mistake even sparkys make mistakes sometimes. cos i have one next door thats made a few & he's been doing it for 30+ years & its my first time i've stuffed up & ive done a fair bit of rewiring around my place over the years.. anyway ive fully rewired it all with 3 core & its all working 100% now, sure if it was major worked need to be done i would get a sparky but minor work aint worth paying for IMO ..

  • #14
    Junior Member Stimpy's Avatar
    Join Date
    Jan 2008
    Location
    SE Melbourne
    Posts
    70
    Thanks
    11
    Thanked 7 Times in 6 Posts
    Rep Power
    202
    Reputation
    60

    Default

    Quote Originally Posted by KRINGLE View Post
    so its a minor mistake even sparkys make mistakes sometimes.
    No we don't and if we do its normally only once!


    Quote Originally Posted by KRINGLE View Post
    anyway ive fully rewired it all with 3 core & its all working 100% now, sure if it was major worked need to be done i would get a sparky but minor work aint worth paying for IMO ..
    But I bet you'll still front up, hand outstretched to the insurance co after someone plugs in a diff appliance that pulls too much giddy up for your 3 core flex to handle and burns down ya dunny.
    Disclaimer
    Any resemblance to real persons, living or dead is purely coincidental. Use only as directed. Apply only to affected area.
    If condition persists, consult your physician. Subject to change without notice. Please remain seated until the ride has
    come to a complete stop. Contains a substantial amount of non-tobacco ingredients. For office use only. Do not write below
    this line. STIMPY WAS HERE. Reproduction strictly prohibited. No solicitors. No anchovies unless otherwise specified.

  • #15
    Junior Member
    Join Date
    Jan 2008
    Location
    Melbourne
    Posts
    33
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    200
    Reputation
    11

    Default

    yer right 3core flex i'm not that stupid its the proper stuff sparkys use that can handle 30amps np ..

  • #16
    Junior Member Stimpy's Avatar
    Join Date
    Jan 2008
    Location
    SE Melbourne
    Posts
    70
    Thanks
    11
    Thanked 7 Times in 6 Posts
    Rep Power
    202
    Reputation
    60

    Default

    Quote Originally Posted by KRINGLE View Post
    yer right 3core flex i'm not that stupid its the proper stuff sparkys use that can handle 30amps np ..
    ohh ok np then.. just when you do the joins make sure you twist em at least twice before you put the masking tape around. oh and if ya have problems with the fuse blowing dont worry stick a six inch nail in the bugger, that'll fix it fer sure.
    Disclaimer
    Any resemblance to real persons, living or dead is purely coincidental. Use only as directed. Apply only to affected area.
    If condition persists, consult your physician. Subject to change without notice. Please remain seated until the ride has
    come to a complete stop. Contains a substantial amount of non-tobacco ingredients. For office use only. Do not write below
    this line. STIMPY WAS HERE. Reproduction strictly prohibited. No solicitors. No anchovies unless otherwise specified.

  • #17
    Senior Member BCNZ's Avatar
    Join Date
    Jan 2008
    Location
    In the back of a 50 kW AM broadcast transmitter
    Posts
    1,697
    Thanks
    235
    Thanked 292 Times in 190 Posts
    Rep Power
    305
    Reputation
    2546

    Default

    Oooh... don't forget to tell your dog not to piss on the cable or it might blow its balls off

  • #18
    Junior Member
    Join Date
    Jan 2008
    Location
    Melbourne
    Posts
    33
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    200
    Reputation
    11

    Default

    i use solid safety bolts cos the nails blow after time

  • #19
    Senior Member
    best4less's Avatar
    Join Date
    Jan 2008
    Location
    Australia
    Posts
    7,684
    Thanks
    3,487
    Thanked 2,207 Times in 1,132 Posts
    Rep Power
    758
    Reputation
    15165

    Default

    Quote Originally Posted by Stimpy View Post
    ohh ok np then.. just when you do the joins make sure you twist em at least twice before you put the masking tape around. oh and if ya have problems with the fuse blowing dont worry stick a six inch nail in the bugger, that'll fix it fer sure.
    If you don't have any masking tape just use some tin foil (not)
    When you do things right, people won't be sure that you have done anything at all

  • #20
    Junior Member Stimpy's Avatar
    Join Date
    Jan 2008
    Location
    SE Melbourne
    Posts
    70
    Thanks
    11
    Thanked 7 Times in 6 Posts
    Rep Power
    202
    Reputation
    60

    Default

    Hey Kringle you didnt happen to do this job as well?

    Disclaimer
    Any resemblance to real persons, living or dead is purely coincidental. Use only as directed. Apply only to affected area.
    If condition persists, consult your physician. Subject to change without notice. Please remain seated until the ride has
    come to a complete stop. Contains a substantial amount of non-tobacco ingredients. For office use only. Do not write below
    this line. STIMPY WAS HERE. Reproduction strictly prohibited. No solicitors. No anchovies unless otherwise specified.

  • Page 1 of 2 12 LastLast

    Similar Threads

    1. LPG conversion problem
      By z80 in forum Automotive Technology
      Replies: 37
      Last Post: 22-02-08, 08:06 PM
    2. Strange Pixelation Problem
      By checkitout in forum Dreambox
      Replies: 15
      Last Post: 15-02-08, 10:52 AM
    3. Strange Lappie Issue
      By navy blue in forum PC Hardware and Printers (including 3D Printers)
      Replies: 4
      Last Post: 11-01-08, 08:14 AM
    4. Strange HDD problem
      By slick1 in forum PC Hardware and Printers (including 3D Printers)
      Replies: 5
      Last Post: 10-01-08, 10:16 AM
    5. Log In Problem
      By SGCPRECEPT in forum Support Ticket System
      Replies: 1
      Last Post: 05-01-08, 07:11 AM

    Bookmarks

    Posting Permissions

    • You may not post new threads
    • You may not post replies
    • You may not post attachments
    • You may not edit your posts
    •