    Default Concept - Direct Card Entry

    Hi All,

    I have a concept 4000 system - works perfectly with site cards from our pool, however, I have been trying to program in fobs, which are not from our card pool; via Direct Entry and Credit Card, by presenting them at the designated reader.

    The panel reads and copies the card data, and its visible in the terminal and insight, however, when trying to use the card, the card is rejected, and 'Invalid Site Code' is printed in the log.

    This has never been an issue on Tecom systems with IUM modules, however, I can't for the life of me get this to work!

    Any ideas would be much appreciated.

    Cheers and thanks in advance



Look Here ->
  • #2
    Junior Member
    Join Date
    Jun 2009
    Age
    46
    Posts
    45
    Thanks
    1
    Thanked 1 Time in 1 Post
    Rep Power
    181
    Reputation
    20

    Default

    the boys at CSD tech a call

    1300 319 499, leave a voicemail if you need to

  • #3
    Junior Member
    Join Date
    Apr 2010
    Posts
    8
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    Thanks for the reply

    Whats the charge for this service?

  • #4
    Member
    Join Date
    Aug 2010
    Location
    NE Vic
    Age
    38
    Posts
    304
    Thanks
    27
    Thanked 27 Times in 23 Posts
    Rep Power
    179
    Reputation
    160

    Default

    Quote Originally Posted by weedle101 View Post
    Thanks for the reply

    Whats the charge for this service?
    You dignity.
    nah they are ok.

  • #5
    Senior Member
    intelliGEORGE's Avatar
    Join Date
    Jan 2008
    Location
    Sydney, AUSTRALIA
    Age
    43
    Posts
    4,106
    Thanks
    884
    Thanked 1,484 Times in 691 Posts
    Rep Power
    478
    Reputation
    7236

    Default

    Whilst direct entry is a feature of the concept system, you still need to tell the system what the site code is, hence the invalid site code error.

    Depending on your memory configuration you can enter up to 128 different site codes. You need to work our what the site code is for the direct entry cards and create a new site code in the system [Menu 2, 5].
    Last edited by intelliGEORGE; 15-02-12 at 06:43 PM.

  • The Following User Says Thank You to intelliGEORGE For This Useful Post:

    weedle101 (16-02-12)

  • #6
    Member
    Join Date
    Jan 2008
    Posts
    255
    Thanks
    35
    Thanked 27 Times in 26 Posts
    Rep Power
    213
    Reputation
    360

    Default

    You cant mix site code and direct entry on the same door.

    You will have to set them to site code as already said

  • The Following User Says Thank You to Andrewpv01 For This Useful Post:

    weedle101 (16-02-12)

  • #7
    Junior Member
    Join Date
    Apr 2010
    Posts
    8
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    Got it working

    Thanks for you help guys, managed to get the site got from MENU 4-5, entered that in, keyed in the number on the card and bam, working like a charm, no need to direct entry the card.

    In what situation can you get the 'Direct Entry' mode to work like the Tecom with IUM? Dont need it in my facility, just asking out of curiosity.

    Thanks again!

  • #8
    Junior Member
    Join Date
    Apr 2010
    Posts
    8
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    Legend!

  • #9
    Junior Member
    Join Date
    Apr 2008
    Location
    WA
    Age
    54
    Posts
    222
    Thanks
    17
    Thanked 35 Times in 27 Posts
    Rep Power
    206
    Reputation
    246

    Default

    Quote Originally Posted by weedle101 View Post
    In what situation can you get the 'Direct Entry' mode to work like the Tecom with IUM? Dont need it in my facility, just asking out of curiosity.

    Thanks again!
    The reader module properties for that door need to be set to direct entry for it to work.

  • #10
    Junior Member
    Join Date
    Jun 2009
    Age
    46
    Posts
    45
    Thanks
    1
    Thanked 1 Time in 1 Post
    Rep Power
    181
    Reputation
    20

    Default

    Quote Originally Posted by weedle101 View Post
    Thanks for the reply

    Whats the charge for this service?
    Haven't seen a charge yet for a basic call like this would be for the techs

    Obviously it's not going to be possible to teach someone from scratch how to do everything over the phone (as some do seem to expect), but most calls are answered pretty quickly , and are pretty quick to answer