    Default Smoke Beams

    Hi Team,

    Any one had any experience installing, servicing smoke beams, this model in particular



    It's wired to a concept 4000 and it's giving 'trouble alarms'

    After looking at the wiring diagram and seeing how it's been wired on site there may be something amiss...?

    There is currently one zone wired into the NC input on the T3 terminal (for trouble alarms) and one zone wired into the T1 and T2, NO input on the T4 terminal for the smoke alarm.

    My question is: are the beams independent of each other, with the top beam on T1 and T2 and the bottom on T3 and T4 so should there be another zone wired into the T3 and T4 input on Terminal 4 for correct operation.

    Any help on this would be appreciated



Look Here ->
  • #2
    Member
    Join Date
    May 2010
    Posts
    409
    Thanks
    15
    Thanked 100 Times in 80 Posts
    Rep Power
    200
    Reputation
    893

    Default

    The site wouldnt been a NSW School Site?

  • #3
    Member AdRock's Avatar
    Join Date
    Aug 2011
    Posts
    330
    Thanks
    167
    Thanked 45 Times in 43 Posts
    Rep Power
    174
    Reputation
    450

    Default

    Quote Originally Posted by bet2win View Post
    The site wouldnt been a NSW School Site?
    No in S.A.

  • #4
    Member
    Join Date
    May 2010
    Posts
    409
    Thanks
    15
    Thanked 100 Times in 80 Posts
    Rep Power
    200
    Reputation
    893

    Default

    Check out the following PDF file that might help


  • The Following User Says Thank You to bet2win For This Useful Post:

    AdRock (11-04-12)

  • #5
    Member AdRock's Avatar
    Join Date
    Aug 2011
    Posts
    330
    Thanks
    167
    Thanked 45 Times in 43 Posts
    Rep Power
    174
    Reputation
    450

    Default

    that link doesnt appear to be working

  • #6
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    907
    Thanks
    156
    Thanked 146 Times in 133 Posts
    Rep Power
    276
    Reputation
    2409

    Default

    link worked for me.

  • #7
    Senior Member
    Join Date
    Jan 2008
    Posts
    701
    Thanks
    13
    Thanked 51 Times in 40 Posts
    Rep Power
    226
    Reputation
    257

    Default

    without reading to much of the manual heres a little info for you regarding smoke beams:

    if you block the sensor completly it will go into fault not fire
    if the lens get dirty it will go into fault
    you need to block approx 70% of the lens to get it to go into fire

  • #8
    Member AdRock's Avatar
    Join Date
    Aug 2011
    Posts
    330
    Thanks
    167
    Thanked 45 Times in 43 Posts
    Rep Power
    174
    Reputation
    450

    Default

    Quote Originally Posted by Chimp View Post
    without reading to much of the manual heres a little info for you regarding smoke beams:

    if you block the sensor completly it will go into fault not fire
    if the lens get dirty it will go into fault
    you need to block approx 70% of the lens to get it to go into fire
    yep, realise all that, i can read the manual too.

    One of the problems is that as they are a latching device when they arm / disarm the area the power is cycled. When the power go's off it causes a trouble alarm, which is fine, but sometimes.... not all the time the trouble restoral doesn't come through and the client gets called for this, which is becoming a bit irritating.

    I've done cable testing and it's not a cabling issue, hoping someone has had some "hands on experience" with these

  • #9
    Member AdRock's Avatar
    Join Date
    Aug 2011
    Posts
    330
    Thanks
    167
    Thanked 45 Times in 43 Posts
    Rep Power
    174
    Reputation
    450

    Default

    Quote Originally Posted by bet2win View Post
    Check out the following PDF file that might help

    Cheers, got it, had to update

    The wiring diagram on that is much better than the manuals.