    Default Tecom - event code 142

    I noticed at the cms that some clients get a CID event 142 alarm (polling loop short) after Remote Log in (Successful Upload).

    What is this?

    I think it may be to do with client or the client's own tech doing some local programming.

    Is it something to do with a voltage drop once someone disconnects?



Look Here ->
  • #2
    Junior Member
    Join Date
    Jan 2008
    Posts
    203
    Thanks
    42
    Thanked 11 Times in 7 Posts
    Rep Power
    206
    Reputation
    70

    Default

    AS far as i know the TECOM doesn't use event code of 142, the event code would 143 Exp Module Fail or 140 General Alarm, but if the zone was E 150 00 C142 then it would be time changed.

    If a tech or client enter menu 19 then it would come with a code of E15000C146 Enter Program Mode.
    Last edited by sirporky; 10-10-12 at 01:23 PM.

  • #3
    Junior Member
    Join Date
    Nov 2010
    Location
    EAST MELBOURNE
    Posts
    56
    Thanks
    8
    Thanked 10 Times in 8 Posts
    Rep Power
    166
    Reputation
    65

    Default

    Thanks SIRPORKY,
    This makes sense given the recent daylight savings. All I know is that it came as an alarm. I may have misread it but i thought it was event code 142.