    Default concept 3000 test reports???

    HI

    I have set daily test reports on a concept 3000 I looked through the manual I can't find it.
    ANy steps to setup???



Look Here ->
  • #2
    Senior Member
    intelliGEORGE's Avatar
    Join Date
    Jan 2008
    Location
    Sydney, AUSTRALIA
    Age
    43
    Posts
    4,106
    Thanks
    884
    Thanked 1,484 Times in 691 Posts
    Rep Power
    478
    Reputation
    7236

    Default Re: concept 3000 test reports???

    There are two things you need to program.

    First a Time Zone [MENU, 5, 2]

    Select a Time Zone and program an appropriate name. e.g. “Time Report” or “Test Report”.
    Program the first Time Zone period to define when the Time Report will be sent.
    Program the Valid Days of the week for the first Period. i.e. Days when the function is required to send the test signal.
    Assign the Holiday Types to be obeyed. (If necessary)

    e.g. Time Report to be sent at 3 AM every night.
    1st Period:03:00-to-03:02
    Days:SMTWTFSH all set to Yes.

    Set Time Zone Function to “Trigger Time Report”.
    This causes the “Time Report” System Input (C01:S18) to be triggered when the Time Zone goes Valid and/or Invalid according to the following settings.

    Set Control Options for Trigger Time Report. [ O F o f ]
    This detemines how the Time Report System Input will be triggered. (C01:S18)
    -O. Time Report System Input On (Alarm edge) when TimeZone goes Valid.
    -F. Not used for this function.
    -o. Not used for this function.
    -f. Not used for this function.

    Second, you'll need to assign the Time Report System Input (C01:S18) to an Area. [MENU, 7, 1]

    Assign Input C01:S18 to the System Area.
    Assign the Time Test Report process group to that input.

    There you have it. Every morning at 3am C01:S18 will trigger the dialer to send a test report back to base.


    Sent from my GT-P5100 using Tapatalk 2