    Default tecom door unlocking on arm????????

    Hi

    I have this system tecom the client armed system badge the reader(Door 18) and three swip it goes red and arms area 2 but the lock door 18 goes unlock????
    QAny ideas why????



Look Here ->
  • #2
    Senior Member

    Join Date
    May 2010
    Posts
    2,106
    Thanks
    252
    Thanked 839 Times in 515 Posts
    Rep Power
    368
    Reputation
    6489

    Default

    Area secured event flag for that area is likely the culprit. Also check the relay mapping for that door. I think you'll find a convenient corelation.
    Last edited by Drift; 07-12-12 at 07:23 PM.

  • #3
    Junior Member
    Join Date
    Nov 2012
    Location
    Brisbane
    Posts
    7
    Thanks
    0
    Thanked 1 Time in 1 Post
    Rep Power
    0
    Reputation
    20

    Default

    Can you clarify - does the door unlock and stay unlocked? Say, until you disarm the area?

    Or does it unlock for the unlock time and relock again?

    Being on a 4 door controller (Door 18), it won't be a relay mapping issue in the traditional sense as none of the Challenger panel event flags can be mapped to a door controller relay. These relays can only be controlled by the event flags of the macro logic functions within that controller - all predefined.

    It's more likely that you have a macro working in reverse - looking at Area Secure condition.