    Default Earthwise Power Saver devise scam.

    A report on Sydney's ch 7 News told of a recent scam of a devise claimed to save '35% off your Electricity Bill'
    The devise was being sold door to door and if I heard right, if you paid cash up front, it ONLY cost $1400 !!!
    On TP, it was $2000.............

    The unit labeled EarthWise Power Saver is coloured green (what else) and is the size of a small inverter with fins on the side.

    They didnt go into details on how this was to work but testing of the devise revealed it actually USED power, not saved it.

    The Company has been closed and all their stock confiscated, at least in NSW as I dont know if this was the NSW Consumer Affairs Department or the Commonwealth.

    The report went onto say it is doubtfull any one who may have purchased this devise will ever get any refund.
    I stand unequivicably behind everything I say , I just dont ever remember saying it !!

  2. The Following User Says Thank You to gordon_s1942 For This Useful Post:

    beer4life (19-12-13)



Look Here ->
  • #2
    Member GavinSV's Avatar
    Join Date
    Jan 2008
    Location
    Adelaide
    Posts
    430
    Thanks
    84
    Thanked 114 Times in 59 Posts
    Rep Power
    234
    Reputation
    1124

    Default

    Hhmmm. Looks like a similar deal is being flogged on feebay
    “There are 10 types of people in this world, those who understand binary – and those who don’t”

  • #3
    Senior Member
    freakee1's Avatar
    Join Date
    Jan 2008
    Location
    somewhere warmer
    Posts
    1,439
    Thanks
    227
    Thanked 768 Times in 405 Posts
    Rep Power
    429
    Reputation
    9214

    Default

    hmmmmmmm most likely correction, which is useless if you are being charged kw/h from your local retailer. MacDonalds and other large business' can save if billed monthly at kVar on a demand tariff.

    Not sure if the new range of smart meters that are being installed look at power factor in the Mainland, but there is nothing here for the domestic customer in Tassie



    f
    有段者

  • #4
    Premium Member

    Join Date
    Jan 2008
    Location
    Central Tablelands of NSW
    Age
    81
    Posts
    13,824
    Thanks
    1,242
    Thanked 3,806 Times in 2,525 Posts
    Rep Power
    1797
    Reputation
    56986

    Default

    How similar these two devices are I have no idea so they cant be compared with any accuracy.
    Obviously there is a huge price difference with the US device selling for $150 and the now discredited Earthwise one for $1400.
    I have no idea what the consumer Laws are in the USA but they are far laxer than ours from what I have seen allowing often ridiculous claims being made regarding the value of the products being sold.

    There is only one way I know that works every time to save power and that is the OFF switch !!!!

    My only knowledge of 'Power factor' comes from an electrician who told me that over a period of time, he had removed capacitors from a series of fluorescent lights as they had failed he thought in a shop and one day the meter/fuse board starting smoking !!!
    Apparently with the capacitors removed, this caused a rise in power/current flow? and that overheated the wiring and it began smoking, fortunately it was seen early and it didnt catch fire and burn the place down.
    I stand unequivicably behind everything I say , I just dont ever remember saying it !!

  • #5
    Senior Member
    Uncle Fester's Avatar
    Join Date
    Jan 2008
    Location
    Commonly found in a pantry or the bottom of a fridge, searching for grains, fermented or distilled
    Posts
    6,405
    Thanks
    2,289
    Thanked 4,414 Times in 2,517 Posts
    Rep Power
    2046
    Reputation
    81778

    Default

    Yes the supply and wiring has to deliver that extra load even though it is "virtual"

    Those cheap power meters that you can get at Jaycar, etc can not differentiate real from reactive power, so a capacitor (what is likely the content of those magic power savers and in most cases pretty useless) will show power consumption although there is practically none.

    I asked the question if reactive is metered a year or two ago on this forum after a similar scam device was promoted on "Current Affair".
    The general consensus was 'no' back then but with the newer meters installed these days and regulations that might be constantly changing quietly behind our backs to maximise profits, one never knows.
    Switched mode power supplies that every device uses these days can have poor power factors that are difficult to compensate.
    Update: A deletion of features that work well and ain't broke but are deemed outdated in order to add things that are up to date and broken.
    Compatibility: A word soon to be deleted from our dictionaries as it is outdated.
    Humans: Entities that are not only outdated but broken... AI-self-learning-update-error...terminate...terminate...

  • #6
    Premium Member

    Join Date
    Jan 2008
    Location
    Central Tablelands of NSW
    Age
    81
    Posts
    13,824
    Thanks
    1,242
    Thanked 3,806 Times in 2,525 Posts
    Rep Power
    1797
    Reputation
    56986

    Default

    In my posting about the over heating wiring, in one way I was wrong when I said the fellow concerned was an 'Electrician' as he would be today.
    He was actually a 'serviceman' employed at the local 'Sell everything from a Needle to an Elephant' family run department store and he serviced their electrical appliances and transitioned from Radio into TV when it was introduced.

    I am not suggesting he wasnt competent in what he did by any means but this side of the trade back then (post WW2) would have been a separate course mostly for Contractors and Industrial Electricians and generally not encounted by him in his daily work.

    I think the rules have changed today but pre 2000, there were many who were classed as 'Electricians' but were generally engaged in low voltage systems and were not certified to work on 'Mains' (240V) and unless they did a 'Bridging Course', could not wire a house or any service other than 'Home Lighting' systems either AC or DC over 32 Volt.
    Last edited by gordon_s1942; 21-12-13 at 11:16 AM.
    I stand unequivicably behind everything I say , I just dont ever remember saying it !!

  • #7
    Junior Member
    Join Date
    Jan 2008
    Posts
    230
    Thanks
    12
    Thanked 44 Times in 28 Posts
    Rep Power
    211
    Reputation
    309

    Default

    power factor correction using capacitor banks as freakee1 has pointed out can save a fortune for large commercial energy customers, with peak demand metering, especially if they have a large inductive load, eg a Supermarket with lots of compressors etc for the refrigeration, but for a domestic situation, completely useless and a waste of money.

  • #8
    Senior Member Svenok's Avatar
    Join Date
    Jan 2008
    Location
    Why alla
    Age
    58
    Posts
    685
    Thanks
    484
    Thanked 263 Times in 101 Posts
    Rep Power
    266
    Reputation
    2335

    Default

    power factor correcting units are huge money savers, most have said if the consumption is huge. At work we have three which helps keep the Pf at .9 which saves a shit load on importing Mvars.
    "It's Life Jim" But Not As We Know It!

    "We come in peace" shoot to kill.

  • The Following User Says Thank You to Svenok For This Useful Post:

    slicker (20-01-21)

  • #9
    Junior Member
    Join Date
    Jul 2017
    Location
    Victoria, Melbourne, Sunshine
    Posts
    2
    Thanks
    5
    Thanked 2 Times in 2 Posts
    Rep Power
    0
    Reputation
    50

    Default PF (Power Factor) Correction for the home? +582% error in Electronic meters

    Quote Originally Posted by Svenok View Post
    power factor correcting units are huge money savers, most have said if the consumption is huge. At work we have three which helps keep the Pf at .9 which saves a shit load on importing Mvars.


    The problem with electronic meters reading incorrectly explains why PF correction works in the home.
    PF correction is just a bunch of large capacitors which clean up the power.
    Cleaning the power allows the meters to read correctly... saving power.

    Thus both sides of the debate are right... PF shouldn't work at home... but does because the meters which read the power are over reporting the amount of power being used.


    :-)

  • The Following User Says Thank You to slicker For This Useful Post:

    Uncle Fester (11-07-17)

  • #10
    LSemmens
    lsemmens's Avatar
    Join Date
    Dec 2011
    Location
    Rural South OZ
    Posts
    10,585
    Thanks
    11,867
    Thanked 7,061 Times in 3,338 Posts
    Rep Power
    3153
    Reputation
    132592

    Default

    Holy thread resurrection batman, what are YOU selling?
    I'm out of my mind, but feel free to leave a message...

  • #11
    Senior Member
    Uncle Fester's Avatar
    Join Date
    Jan 2008
    Location
    Commonly found in a pantry or the bottom of a fridge, searching for grains, fermented or distilled
    Posts
    6,405
    Thanks
    2,289
    Thanked 4,414 Times in 2,517 Posts
    Rep Power
    2046
    Reputation
    81778

    Default

    I don't think he is selling anything. That link is legit from a Dutch university.
    Finally after 3 and a half years somebody responded to my questioning in post #5 in regards to the newer (smart)meters and switched mode loads.
    Last edited by Uncle Fester; 11-07-17 at 11:28 AM.
    Update: A deletion of features that work well and ain't broke but are deemed outdated in order to add things that are up to date and broken.
    Compatibility: A word soon to be deleted from our dictionaries as it is outdated.
    Humans: Entities that are not only outdated but broken... AI-self-learning-update-error...terminate...terminate...

  • The Following User Says Thank You to Uncle Fester For This Useful Post:

    slicker (20-01-21)

  • #12
    Premium Member
    Skepticist's Avatar
    Join Date
    Apr 2009
    Posts
    1,139
    Thanks
    714
    Thanked 670 Times in 525 Posts
    Rep Power
    475
    Reputation
    12780

    Default

    There is a recognised problem with electronic power supplies (SMPS) and electronic 'smart' meters which due to the meter's inadequate determination of RMS values of a distorted sine wave. Conventional disc type meters are not as susceptible to inaccuracies caused by distorted waveforms.

    The solution is for 'smart' meters to be made somewhat smarter in the way they determine the true RMS values of voltage and current and it could be done but at the expense of reduced revenue of course.

  • The Following User Says Thank You to Skepticist For This Useful Post:

    slicker (20-01-21)

  • #13
    Administrator
    admin's Avatar
    Join Date
    Jan 2008
    Location
    Victoria
    Age
    56
    Posts
    31,150
    Thanks
    2,238
    Thanked 13,731 Times in 5,823 Posts
    Rep Power
    4552
    Reputation
    165805

    Default

    Quote Originally Posted by nomeat View Post
    I don't think he is selling anything. That link is legit from a Dutch university.
    Finally after 3 and a half years somebody responded to my questioning in post #5 in regards to the newer (smart)meters and switched mode loads.
    Better late than never

  • The Following User Says Thank You to admin For This Useful Post:

    slicker (20-01-21)

  • #14
    Senior Member
    fromaron's Avatar
    Join Date
    Jan 2008
    Posts
    2,133
    Thanks
    268
    Thanked 732 Times in 387 Posts
    Rep Power
    543
    Reputation
    13794

    Default

    Switched mode power supplies, LED lighting etc introduce more capacitive load so those so called capacitive power factor correction units are making things worse, not better.
    There are at least commercial power factor correction units where instead of capacitors the unit varies inductance to compensate for the PF change from lagging to leading.

  • The Following User Says Thank You to fromaron For This Useful Post:

    slicker (20-01-21)

  • #15
    Junior Member
    Join Date
    Jul 2017
    Location
    Victoria, Melbourne, Sunshine
    Posts
    2
    Thanks
    5
    Thanked 2 Times in 2 Posts
    Rep Power
    0
    Reputation
    50

    Default IEE publication: +582% error in smart meters

    The article appeared in an IEEE journal.



    :-)
    Last edited by slicker; 20-01-21 at 03:42 PM.