    We are doing a job which has smoke doors which has maglocks on then.
    Problem is what are the rules concerning then in the event of fire. In the event of a fire the smoke doors release from the fire panel but when they shut the maglock grab the doors, i though in the event of a fire in each of the door controllers they should have a relay which drops open releasing the power to the maglocks. The job is Vic any thoughs.



Look Here ->
  • #2
    Junior Member
    Join Date
    Jul 2009
    Location
    Brisbane
    Posts
    74
    Thanks
    4
    Thanked 9 Times in 9 Posts
    Rep Power
    182
    Reputation
    80

    Default

    Up in QLD the setup up we use for fire/smoke doors is a relay (either 12vDC 0r 24vDC depends on the fire panel) in the door controller.

    We set the relay up in a fail-safe configuration so that when there are no alarms the relay is energised (the feed to the relay is from the fire panel) so if the cable gets cut, disconnected, burnt or there’s an actual fire alarm it drops the power to the relay which than goes open to drop the power to the mag locks. You might also want to think about installing an emergency glass break at the doors

  • #3
    Junior Member pjjp123's Avatar
    Join Date
    May 2009
    Age
    59
    Posts
    67
    Thanks
    11
    Thanked 2 Times in 2 Posts
    Rep Power
    184
    Reputation
    20

    Default

    The mag locks hold the doors open and in the event of a fire they release and let the doors close,if they are double doors there is a requirement that a single test switch shall be installed to release both doors (as1670.1 I think).

  • #4
    Senior Member
    downunderdan's Avatar
    Join Date
    Sep 2008
    Location
    Sydney Metropolitan
    Posts
    2,497
    Thanks
    163
    Thanked 601 Times in 422 Posts
    Rep Power
    365
    Reputation
    4649

    Default

    Wait.

    Maglocks and holdbacks are not the same thing (even though they work similarly).

  • #5
    Junior Member
    Join Date
    Apr 2008
    Location
    WA
    Age
    54
    Posts
    222
    Thanks
    17
    Thanked 35 Times in 27 Posts
    Rep Power
    206
    Reputation
    246

    Default

    I am assuming the doors are sometimes closed, so just disabling the maglocks is not an option.
    Generally I used to wire in an input to the concept to activate a door lock/unlock list.
    The doors all had break glass as a backup release or relay on the power supply as per "2secure".

    EDit: I have seen some "consultants" call holdbacks maglocks, if its just a plan lock carefully at their indicated position.
    Last edited by Privatteer; 09-05-12 at 12:07 AM.

  • #6
    Junior Member pjjp123's Avatar
    Join Date
    May 2009
    Age
    59
    Posts
    67
    Thanks
    11
    Thanked 2 Times in 2 Posts
    Rep Power
    184
    Reputation
    20

    Default

    Sorry about the confusion ,but the consultants I work under (Sydney to QLD border) call holdbacks "Magnomatic door release" hence maglocks and your actual padde type door lock as a ES or Electric Strike.

  • #7
    Senior Member bss904's Avatar
    Join Date
    Jan 2008
    Location
    NOT in Thailand
    Posts
    1,110
    Thanks
    523
    Thanked 251 Times in 153 Posts
    Rep Power
    294
    Reputation
    2964

    Default

    Quote Originally Posted by pjjp123 View Post
    Sorry about the confusion ,but the consultants I work under (Sydney to QLD border) call holdbacks "Magnomatic door release" hence maglocks and your actual padde type door lock as a ES or Electric Strike.
    and have a guess what we call consultants, ooh just realised that I can't use that sort of language here.

  • #8
    Junior Member pjjp123's Avatar
    Join Date
    May 2009
    Age
    59
    Posts
    67
    Thanks
    11
    Thanked 2 Times in 2 Posts
    Rep Power
    184
    Reputation
    20

    Default

    Quote Originally Posted by bss904 View Post
    and have a guess what we call consultants, ooh just realised that I can't use that sort of language here.
    yep the job im on at the moment is up to revision S which is like 20 changes ,,, a 3 storey building with concrete slabs and about 500 smoke detectors,,not easy to move things around Mr consultant

  • #9
    Junior Member pjjp123's Avatar
    Join Date
    May 2009
    Age
    59
    Posts
    67
    Thanks
    11
    Thanked 2 Times in 2 Posts
    Rep Power
    184
    Reputation
    20

    Default

    Quote Originally Posted by bss904 View Post
    and have a guess what we call consultants, ooh just realised that I can't use that sort of language here.
    yep the job im on at the moment is up to revision S which is like 20 changes ,,, a 3 storey building with concrete slabs and about 500 smoke detectors,,not easy to move things around Mr consultant

  • #10
    Senior Member
    downunderdan's Avatar
    Join Date
    Sep 2008
    Location
    Sydney Metropolitan
    Posts
    2,497
    Thanks
    163
    Thanked 601 Times in 422 Posts
    Rep Power
    365
    Reputation
    4649

    Default

    Oy! I'm a consultant.

    You know, from the root words Con and Insult. As in "I am here to consult you".

    I feel so dirty...

  • #11
    Member
    Join Date
    Aug 2010
    Location
    NE Vic
    Age
    38
    Posts
    304
    Thanks
    27
    Thanked 27 Times in 23 Posts
    Rep Power
    179
    Reputation
    160

    Default

    I am not 100% sure on requirements but I think that it must be Fail Safe and on a relay off the FIP.
    It needs to be a mechanical switching not software driven.

  • The Following 2 Users Say Thank You to Uncle Kneebo For This Useful Post:

    ds2020 (16-05-12),sirporky (14-05-12)