    Default Automatic Transfer Switch / Generator Starter

    Does anyone know if such a device is available here in Australia ?

    I want to set up a backup generator for when there is a blackout, so I need to automatically start the generator ( which has electric start ) and isolate from the grid until power is restored to normal and then stop generator.
    The house is only single phase.

    Have seen a couple of these things around for swithing from inverter to generator as used in boats etc but nothing I cant find anything for Generator / mains switching .



Look Here ->
  • #2
    Premium Member rob916's Avatar
    Join Date
    Apr 2008
    Location
    Bargara, Queensland.
    Age
    52
    Posts
    1,573
    Thanks
    49
    Thanked 75 Times in 36 Posts
    Rep Power
    250
    Reputation
    248

    Default

    You should be able to do this with contactors.
    What happens if I press alt + F4?

  • #3
    Senior Member
    Join Date
    Feb 2008
    Posts
    831
    Thanks
    174
    Thanked 434 Times in 193 Posts
    Rep Power
    269
    Reputation
    2277

    Default

    Quote Originally Posted by rob916 View Post
    You should be able to do this with contactors.
    Yeah I could make my own using a large DPDT relay with 240 coil and small timer circuit to trigger generator but this wont be approved and will void house insurance if there is ever an electrical fire , electrocution etc .

  • #4
    Premium Member rob916's Avatar
    Join Date
    Apr 2008
    Location
    Bargara, Queensland.
    Age
    52
    Posts
    1,573
    Thanks
    49
    Thanked 75 Times in 36 Posts
    Rep Power
    250
    Reputation
    248

    Default

    Let me rephrase, A licensed sparky should be able to do this with contactors for you.
    Search for backup generator control module.
    or this at the bottom of page.
    What happens if I press alt + F4?

  • #5
    Senior Member BCNZ's Avatar
    Join Date
    Jan 2008
    Location
    In the back of a 50 kW AM broadcast transmitter
    Posts
    1,697
    Thanks
    235
    Thanked 292 Times in 190 Posts
    Rep Power
    304
    Reputation
    2546

    Default

    You can easily make a unit that will start a generator using contactors, but there's more to starting a generator than just operating the starter motor. There are various things to consider, plus the issue of mains change-over.

    The change-over needs a delay on it, so that when mains returns, the system doesn't snap back to the mains immediately.
    It also needs to be able to sense that the generator is delivering stable voltage and frequency before it changes to it.

    The system needs to know that the engine has started, and what to do if it doesn't.
    It needs to be able to shut the engine down once mains has returned and the appropriate delay has timed out.
    There also needs to be monitoring of engine temp, oil pressure, over and under-voltage of the genset and more.
    This is why proper genset control units are used as they have all these functions built in. Have a look on Ebay - I'm sure I have seen them on there.

  • #6
    Senior Member cwispy's Avatar
    Join Date
    Jan 2008
    Location
    In bed sleeping
    Posts
    1,090
    Thanks
    140
    Thanked 296 Times in 114 Posts
    Rep Power
    265
    Reputation
    1581

    Default

    These guys may be able to do what you want.

    What would you do if your server was stolen or failed beyond repair?
    http://www.2000cn.com.au/shadowprotect.html

  • #7
    Senior Member
    Join Date
    Feb 2008
    Posts
    831
    Thanks
    174
    Thanked 434 Times in 193 Posts
    Rep Power
    269
    Reputation
    2277

    Default

    Quote Originally Posted by Studio1 View Post
    You can easily make a unit that will start a generator using contactors, but there's more to starting a generator than just operating the starter motor. There are various things to consider, plus the issue of mains change-over.

    The change-over needs a delay on it, so that when mains returns, the system doesn't snap back to the mains immediately.
    It also needs to be able to sense that the generator is delivering stable voltage and frequency before it changes to it.

    The system needs to know that the engine has started, and what to do if it doesn't.
    It needs to be able to shut the engine down once mains has returned and the appropriate delay has timed out.
    There also needs to be monitoring of engine temp, oil pressure, over and under-voltage of the genset and more.
    This is why proper genset control units are used as they have all these functions built in. Have a look on Ebay - I'm sure I have seen them on there.
    Thanks for the reply mate , I am aware that there needs to be delays etc , hence the question seeking a pre-made unit .
    I have looked at the link Rob provided and these units are for Marine use , contactors are only low current not suitable for switching home mains power.

    I have tried and searched until my finger are almost worn out and cant find anything on eBay or available in Australia that can be simply purchased and connected up by a sparky .
    Heaps of information saying what you need but virtually nothing with the units themselves , countless pages saying you need an Automatic transfer switch or generator control unit , automatic gen starter , you name it there stuff written everywhere but where the hell are any of these units for sale?

  • #8
    Senior Member cwispy's Avatar
    Join Date
    Jan 2008
    Location
    In bed sleeping
    Posts
    1,090
    Thanks
    140
    Thanked 296 Times in 114 Posts
    Rep Power
    265
    Reputation
    1581

    Default

    Quote Originally Posted by Joey View Post
    Heaps of information saying what you need but virtually nothing with the units themselves , countless pages saying you need an Automatic transfer switch or generator control unit , automatic gen starter , you name it there stuff written everywhere but where the hell are any of these units for sale?


    What would you do if your server was stolen or failed beyond repair?
    http://www.2000cn.com.au/shadowprotect.html

  • #9
    Senior Member
    Join Date
    Feb 2008
    Posts
    831
    Thanks
    174
    Thanked 434 Times in 193 Posts
    Rep Power
    269
    Reputation
    2277

    Default

    Quote Originally Posted by cwispy View Post
    These guys may be able to do what you want.

    Have seen these already " Complies with Marine & Mobile Wiring Standards" they dont have a generator starter and will only handle 40amps , would need to be 80amp of higher contactors to start with .
    The average single phase main switch is 80amp

  • #10
    Senior Member cwispy's Avatar
    Join Date
    Jan 2008
    Location
    In bed sleeping
    Posts
    1,090
    Thanks
    140
    Thanked 296 Times in 114 Posts
    Rep Power
    265
    Reputation
    1581

    Default

    Try contacting someone like this then.



    The standby gensets I have had experience with, such as the ones in the radio transmission sites, just have a contact point for the ATS. It simply throws a contact and then genset handles its own startup and turning on the output power when its up to speed, then the ATS switches to that power feed when its stable.
    What would you do if your server was stolen or failed beyond repair?
    http://www.2000cn.com.au/shadowprotect.html

  • #11
    Senior Member z80's Avatar
    Join Date
    Jan 2008
    Posts
    5,840
    Thanks
    112
    Thanked 77 Times in 48 Posts
    Rep Power
    0
    Reputation
    708

    Default

    What's the total power requirement of the generator?

    Is money an issue?

  • #12
    Senior Member
    Join Date
    Feb 2008
    Posts
    831
    Thanks
    174
    Thanked 434 Times in 193 Posts
    Rep Power
    269
    Reputation
    2277

    Default

    Quote Originally Posted by z80 View Post
    What's the total power requirement of the generator?

    Is money an issue?
    Only 4KVA continuous , money isnt an issue for the correct system .

  • #13
    Member
    Join Date
    Jan 2008
    Posts
    391
    Thanks
    27
    Thanked 98 Times in 72 Posts
    Rep Power
    242
    Reputation
    1584

    Default

    Quote Originally Posted by Joey View Post
    Only 4KVA continuous
    4kVA @ 240 Volts is only 16.6 Amps... Correct??

  • #14
    Senior Member
    Join Date
    Feb 2008
    Posts
    831
    Thanks
    174
    Thanked 434 Times in 193 Posts
    Rep Power
    269
    Reputation
    2277

    Default

    Quote Originally Posted by Gitch View Post
    4kVA @ 240 Volts is only 16.6 Amps... Correct??

    Thats correct , but the contactors have to switch back over to normal mains load which is much higher if running bore pump , electric stove , R/C Aircon etc
    Handling the Generator load is not a problem.

  • #15
    Senior Member cwispy's Avatar
    Join Date
    Jan 2008
    Location
    In bed sleeping
    Posts
    1,090
    Thanks
    140
    Thanked 296 Times in 114 Posts
    Rep Power
    265
    Reputation
    1581

    Default

    Have a look at these, specifically the 300SE



    They are part of Emerson Network Power. It would appear that they have all the gear your looking for.

    Edit, look at the lower ones too. I didnt notice they also have generator control. The 300's are 3 phase.
    What would you do if your server was stolen or failed beyond repair?
    http://www.2000cn.com.au/shadowprotect.html

  • #16
    Senior Member cwispy's Avatar
    Join Date
    Jan 2008
    Location
    In bed sleeping
    Posts
    1,090
    Thanks
    140
    Thanked 296 Times in 114 Posts
    Rep Power
    265
    Reputation
    1581

    Default

    Another link to GEC asia pacifics site, but it does not have a lot of details

    What would you do if your server was stolen or failed beyond repair?
    http://www.2000cn.com.au/shadowprotect.html

  • #17
    Senior Member z80's Avatar
    Join Date
    Jan 2008
    Posts
    5,840
    Thanks
    112
    Thanked 77 Times in 48 Posts
    Rep Power
    0
    Reputation
    708

    Default

    Quote Originally Posted by Joey View Post
    Thats correct , but the contactors have to switch back over to normal mains load which is much higher if running bore pump , electric stove , R/C Aircon etc
    Handling the Generator load is not a problem.

    McFarlane generators in Clayton Victoria.


    They can point you in the right direction.





    They have a calculator tool for sizing as well.


  • #18
    Junior Member
    Join Date
    Jan 2008
    Posts
    6
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Smile

    We use one from here

    200 HP diesel/3 phase generator/100 bed hospital.
    Auto switchover, controls 2 contactors, opens the mains supply one, starts engine then closes generator contactor and power available in under 8 seconds, All legal and approved (Not cheap though)