    Default 10 amp plug into a 15 amp socket

    Just bought a new oven, the old one, a SMEG piece of crap will never touch again, had a 15 amp plug and there is a 15 amp socket on the wall. The new oven, a Blanco, cheap as chips don't care if it only lasts 5 years, has a 10 amp plug. Now obviously the plug fits and won't overload the circuit, but can anyone think of any reason why it could be dangerous to connect a 10 amp plug to a 15 amp socket/circuit? Just check the board and it has a dedicated 32 amp breaker on it.



Look Here ->
  • #2
    Administrator
    mtv's Avatar
    Join Date
    Jan 2008
    Posts
    19,908
    Thanks
    7,518
    Thanked 15,074 Times in 6,765 Posts
    Rep Power
    5651
    Reputation
    239465

    Default

    The earth pin on a 15A socket is physically larger than a 10A socket, so a 10A plug in a 15A socket will have a loose-fitting earth connection.

  • The Following User Says Thank You to mtv For This Useful Post:

    eaglem (24-05-20)

  • #3
    Member

    Join Date
    Nov 2015
    Posts
    359
    Thanks
    550
    Thanked 635 Times in 173 Posts
    Rep Power
    368
    Reputation
    12741

    Default

    Yes I thought about that, however the sockets have a sleeve type system that accepts the pin and the active and neutral will hold the plug at the correct height - even so, I might get the socket changed.

    Edit: I might get a 10 amp to 15 amp converter - apparently you can get them from Jaycar - used in caravans quite a bit.
    Last edited by mi_tasol; 13-02-16 at 01:24 PM.

  • #4
    Administrator
    mtv's Avatar
    Join Date
    Jan 2008
    Posts
    19,908
    Thanks
    7,518
    Thanked 15,074 Times in 6,765 Posts
    Rep Power
    5651
    Reputation
    239465

    Default

    I'd just put a 15A plug on the cable.

  • #5
    Senior Member
    Godzilla's Avatar
    Join Date
    Jul 2008
    Location
    Melbourne
    Age
    60
    Posts
    12,742
    Thanks
    16,583
    Thanked 7,203 Times in 3,649 Posts
    Rep Power
    2200
    Reputation
    79153

    Default

    Quote Originally Posted by mtv View Post
    I'd just put a 15A plug on the cable.
    Dont forget the legal clause....get a licensed/qualified person to do it.....

  • The Following User Says Thank You to Godzilla For This Useful Post:

    OSIRUS (15-02-16)

  • #6
    Member

    Join Date
    Nov 2015
    Posts
    359
    Thanks
    550
    Thanked 635 Times in 173 Posts
    Rep Power
    368
    Reputation
    12741

    Default

    Quote Originally Posted by mtv View Post
    I'd just put a 15A plug on the cable.
    Yes that's probably simpler - to have a licensed person put a 15A plug on the cable

  • #7
    Senior Member
    Join Date
    Jan 2008
    Age
    59
    Posts
    669
    Thanks
    477
    Thanked 217 Times in 115 Posts
    Rep Power
    270
    Reputation
    2459

    Default

    It should be fine. We have a 15 amp plug inside for our air con. I use it to charge phones, plug iron in to, anything. As long as the plug of your 10 amp stuff fits in, it should be fine.

  • #8
    Senior Member
    bob_m_54's Avatar
    Join Date
    Jan 2011
    Posts
    2,093
    Thanks
    1,054
    Thanked 1,151 Times in 689 Posts
    Rep Power
    634
    Reputation
    20178

    Default

    OK, I can't find it in as3000, but both 10A and 15A plugs have a 1.5mm thick earth pin that is the same length. The 10A Earth pin is 6.4mm wide, while the 15A Earth pin is 9mm wide. By virtue of the fact that it is physically possible to insert a 10A plug into a 15A socket, there is no problem with with using a 10A plug in a 15A socket. (obviously you can't the other way around). If there was any danger, the plugs and sockets would be made so that it was impossible to do.

    If you have a look at the pic, the 10A plug Earth pin aligns with the centre of the 15A wall plate Earth socket. The Earth socket has a set of contacts that contact either side of the pin, so proper contact is made whether it is a 15A plug or a 10A plug.

  • #9
    Senior Member
    fromaron's Avatar
    Join Date
    Jan 2008
    Posts
    2,136
    Thanks
    270
    Thanked 737 Times in 389 Posts
    Rep Power
    546
    Reputation
    13894

    Default

    You have your new oven with 10 Amp cable and plug un-protected electrically. What you did is generally considered illegal in Australia as the protection devices were rated based on the rated load. That is true, obviously if electrical system in your place was sized by qualified people.
    Imagine you have an overload condition in your oven causing the current to raise to let's say 11Amp. The protection was designed for 15Amp plug and as a result your oven and cable will be subject to the higher current for a long time causing over-heating with potential fire.
    I highly recommend you call a licensed electrician to change the power socket to 10Amp and review the protection device - circuit breaker I assume or even fuse if the house was built long time ago.

  • The Following 5 Users Say Thank You to fromaron For This Useful Post:

    eaglem (24-05-20),enf (13-02-16),Godzilla (13-02-16),lsemmens (13-02-16),Tiny (13-02-16)

  • #10
    Senior Member
    bob_m_54's Avatar
    Join Date
    Jan 2011
    Posts
    2,093
    Thanks
    1,054
    Thanked 1,151 Times in 689 Posts
    Rep Power
    634
    Reputation
    20178

    Default

    Good point fromaron. Although CCT breakers and fuses are sized to protect the wiring, in the case of a stove where the flexible cable is hidden behind the unit, it would be wise to size the CCT breaker to protect this as well. A 15A stove outlet will likely have a 32A fuse or CCT breaker protecting the wiring, but the most he would do is change it for a 20A CCT breaker, unless you specifically ask him to fit a 10A socket as well.

  • #11
    Super Moderator
    enf's Avatar
    Join Date
    Jan 2008
    Location
    Canberra
    Age
    70
    Posts
    17,788
    Thanks
    16,844
    Thanked 35,062 Times in 9,090 Posts
    Rep Power
    13719
    Reputation
    646449

    Default

    Quote Originally Posted by fromaron View Post
    You have your new oven with 10 Amp cable and plug un-protected electrically. What you did is generally considered illegal in Australia as the protection devices were rated based on the rated load. That is true, obviously if electrical system in your place was sized by qualified people.
    Imagine you have an overload condition in your oven causing the current to raise to let's say 11Amp. The protection was designed for 15Amp plug and as a result your oven and cable will be subject to the higher current for a long time causing over-heating with potential fire.
    I highly recommend you call a licensed electrician to change the power socket to 10Amp and review the protection device - circuit breaker I assume or even fuse if the house was built long time ago.
    I seem to remember that this is essentially correct. The protection device (circuit breaker) is designed to protect both the oven AND the in house wiring. Change the socket and breaker.
    The fact that there's a highway to hell and a stairway to heaven says a lot about the anticipated traffic flow.

  • The Following User Says Thank You to enf For This Useful Post:

    gulliver (13-02-16)

  • #12
    Senior Member
    fromaron's Avatar
    Join Date
    Jan 2008
    Posts
    2,136
    Thanks
    270
    Thanked 737 Times in 389 Posts
    Rep Power
    546
    Reputation
    13894

    Default

    Quote Originally Posted by bob_m_54 View Post
    A 15A stove outlet will likely have a 32A fuse or CCT breaker protecting the wiring, but the most he would do is change it for a 20A CCT breaker, unless you specifically ask him to fit a 10A socket as well.
    It is a common practice to use a dedicated oven power point with it's own protection. Also it is important to know some ovens do not like being powered downstream of earth leakage switch so electrician might need to be involved to slightly rewire the switch board.

  • The Following User Says Thank You to fromaron For This Useful Post:

    Tiny (13-02-16)

  • #13
    Senior Member
    Uncle Fester's Avatar
    Join Date
    Jan 2008
    Location
    Commonly found in a pantry or the bottom of a fridge, searching for grains, fermented or distilled
    Posts
    6,412
    Thanks
    2,292
    Thanked 4,420 Times in 2,521 Posts
    Rep Power
    2048
    Reputation
    81898

    Default

    Quote Originally Posted by fromaron View Post
    It is a common practice to use a dedicated oven power point with it's own protection. Also it is important to know some ovens do not like being powered downstream of earth leakage switch so electrician might need to be involved to slightly rewire the switch board.
    I would be concerned too about having a 10A rated device on 32A circuit breaker but why can he not use an RCD?
    If there is earth leakage then there is a fault !
    Update: A deletion of features that work well and ain't broke but are deemed outdated in order to add things that are up to date and broken.
    Compatibility: A word soon to be deleted from our dictionaries as it is outdated.
    Humans: Entities that are not only outdated but broken... AI-self-learning-update-error...terminate...terminate...

  • #14
    Premium Member
    gulliver's Avatar
    Join Date
    Jan 2008
    Location
    Sydney
    Age
    78
    Posts
    1,183
    Thanks
    10,923
    Thanked 341 Times in 234 Posts
    Rep Power
    338
    Reputation
    5032

    Default

    because ovens do have a certain leakage and they are on a fixed wired instalation,due to steam,oil etc they are not required to be on a RCD,.I had to disconnect quite a few because of this,even if there is a clock on the stove the Megger will give you a fault.When I used to work for St.George Ranges a long time ago,even the Inspectors fell for this and given a defect notice.
    Last edited by gulliver; 13-02-16 at 07:01 PM.

  • The Following User Says Thank You to gulliver For This Useful Post:

    fromaron (14-02-16)

  • #15
    Senior Member
    Uncle Fester's Avatar
    Join Date
    Jan 2008
    Location
    Commonly found in a pantry or the bottom of a fridge, searching for grains, fermented or distilled
    Posts
    6,412
    Thanks
    2,292
    Thanked 4,420 Times in 2,521 Posts
    Rep Power
    2048
    Reputation
    81898

    Default

    Quote Originally Posted by gulliver View Post
    because ovens do have a certain leakage and they are on a fixed wired instalation,due to steam,oil etc they are not required to be on a RCD,.I had to disconnect quite a few because of this,even if there is a clock on the stove the Megger will give you a fault.When I used to work for St.George Ranges a long time ago,even the Inspectors fell for this and given a defect notice.
    ..but the OP is not using a fixed wired installation.

    Is it unlawful to use a 2kW oven on a standard 10A GPO in a circuit with a 20A RCD breaker ?

    I would have also assumed that modern stoves might be better designed to deal with steam and oil due to stricter safety regulations these days.

    Arcing from oil bridges around contacts would be a fire hazard for me.
    Update: A deletion of features that work well and ain't broke but are deemed outdated in order to add things that are up to date and broken.
    Compatibility: A word soon to be deleted from our dictionaries as it is outdated.
    Humans: Entities that are not only outdated but broken... AI-self-learning-update-error...terminate...terminate...

  • #16
    Senior Member
    freakee1's Avatar
    Join Date
    Jan 2008
    Location
    somewhere warmer
    Posts
    1,442
    Thanks
    227
    Thanked 770 Times in 406 Posts
    Rep Power
    432
    Reputation
    9254

    Default

    far out......... why not just completely re wire the house while you are at it, just in case

    your Smeg would have been rated at 15A, hence a 15 Amp outlet - the earth pin is bigger purely to stop people bunging 15 Amp appliances in an 10 Amp outlet
    if you pull a powerpoint apart you will find that the connection is a clamp that makes connection when pushing in the plug - so your 6.4mm earth pin is fully covered by a 9mm clamp.

    The earth is designed to remove fault current to earth when something goes wrong for a really short period of time

    just plug it in and use it



    f
    有段者

  • The Following User Says Thank You to freakee1 For This Useful Post:

    Onefella (14-02-16)

  • #17
    Premium Member
    Onefella's Avatar
    Join Date
    Jan 2008
    Location
    Top End
    Posts
    2,063
    Thanks
    1,062
    Thanked 1,360 Times in 678 Posts
    Rep Power
    639
    Reputation
    18622

    Default

    I agree with Freakee. Just plug it in and use it. I would; and I'm a qualified Electrician.

    FYI:

    15A Outlets have a 20A circuit breaker.

    10A Outlets have a 16A circuit breaker.

    Light circuits have a 10A circuit breaker.

  • The Following User Says Thank You to Onefella For This Useful Post:

    gulliver (14-02-16)

  • #18
    Senior Member
    fromaron's Avatar
    Join Date
    Jan 2008
    Posts
    2,136
    Thanks
    270
    Thanked 737 Times in 389 Posts
    Rep Power
    546
    Reputation
    13894

    Default

    Quote Originally Posted by Onefella View Post
    I agree with Freakee. Just plug it in and use it. I would; and I'm a qualified Electrician.

    FYI:

    15A Outlets have a 20A circuit breaker.

    10A Outlets have a 16A circuit breaker.

    Light circuits have a 10A circuit breaker.
    We have no idea how was the 15amp socket wired in a first place so by simply giving such advice you make an assumption which could be wrong and in fact dangerous in some cases.

  • #19
    Senior Member
    bob_m_54's Avatar
    Join Date
    Jan 2011
    Posts
    2,093
    Thanks
    1,054
    Thanked 1,151 Times in 689 Posts
    Rep Power
    634
    Reputation
    20178

    Default

    Quote Originally Posted by fromaron View Post
    It is a common practice to use a dedicated oven power point with it's own protection. Also it is important to know some ovens do not like being powered downstream of earth leakage switch so electrician might need to be involved to slightly rewire the switch board.
    Yes, no argument there..
    Although on rereading my post, I should have said "10A socket instead of the 15A", but that's what I meant. Personally I'd just plug the stove in and use it.. I might even change to a 20A CCT breaker. (Actually, ours is still a fuse anyway)

  • #20
    Senior Member
    bob_m_54's Avatar
    Join Date
    Jan 2011
    Posts
    2,093
    Thanks
    1,054
    Thanked 1,151 Times in 689 Posts
    Rep Power
    634
    Reputation
    20178

    Default

    Quote Originally Posted by Onefella View Post
    I agree with Freakee. Just plug it in and use it. I would; and I'm a qualified Electrician.

    FYI:

    15A Outlets have a 20A circuit breaker.

    10A Outlets have a 16A circuit breaker.

    Light circuits have a 10A circuit breaker.
    My oven 15A outlet has a 32A fuse..