    So the other morning, at 7am, our alarm starts beeping with a fault, saying low battery. Ok, The battery is nearly 4 years old, so time for a new one. But from that same point in time, the outputs have stopped working all together.

    We use the alarm every day and evening (night mode) and also use remote controller to enable the alarm when leaving the premises, which is verified by the strobe light flashing. From the exact day when the "battery low" issue appeared, the outputs stopped working.

    I've restarted the system multiple times with the battery disconnected. I've performed multiple external & internal siren tests and also a strobe test. The alarm panel thinks that it is performing these actions, though there is no output. There is no errors or alerts or no power overloads (not sure what would actually appear in this case).

    I put put the alarm in to an alarming state and put a multimeter on the comm + and out 1, 13.8V, comm+ and out2, 14V, comm+ and N/O only 0.6V.

    I've tried isolating everything, taking everything out of comm+ and adding one it at a time (separately), still no outputs each time. I've also connected the piezo's and strobe directly to the battery, they work. When I does the same with the external siren, it clicks, assuming that this is probably working.

    I'm looking for pointers on what to do next in diagnosis?



Look Here ->
  • #2
    Junior Member Mrsnake82's Avatar
    Join Date
    Mar 2016
    Location
    London
    Posts
    11
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    Did you connect the new battery correctly? Formerly, I saw a similar problem: if you remove the battery the N/O relay is not working.

    Tapatalkkal küldve az én SM-G870F eszközömről

  • #3
    Junior Member
    Join Date
    Mar 2015
    Location
    Queensland
    Posts
    140
    Thanks
    0
    Thanked 13 Times in 11 Posts
    Rep Power
    120
    Reputation
    270

    Default

    The outputs turned off with the low battery because it's a default feature, Menu 4,1,5 - "do not operate on low battery".
    However, it should have reverted back to normal operation once the battery condition was rectified.
    Try 7,9,1 - manual battery test then check your outputs. You might also consider turning that option off in the programming(4,1,5). Failing that it's a default and re-program as your last option

  • The Following 2 Users Say Thank You to Pyro For This Useful Post:

    Gaffa (18-04-16),raytriplej (05-01-17)

  • #4
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    911
    Thanks
    157
    Thanked 147 Times in 134 Posts
    Rep Power
    277
    Reputation
    2429

    Default

    As what Pyro as stated. Outputs are disabled on low battery. But can be changed in programming.

  • The Following User Says Thank You to secure For This Useful Post:

    Gaffa (18-04-16)

  • #5
    Junior Member
    Join Date
    Apr 2016
    Posts
    2
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    Quote Originally Posted by secure View Post
    As what Pyro as stated. Outputs are disabled on low battery. But can be changed in programming.
    Thanks Guys,

    It was exactly that. Off to get a replacement battery tomorrow!