    Default IEC Female plug and lead using 1.0mm sq cable. Is it too small for 800W Max

    I'm very surprise that leads today for UPS that use a IEC Female plug from your power point to the UPS use only a 1.0MM lead and this it rated at 10 amps. you would think they should be at least 1.5MMsq? Can someone tell me a typical extension lead around 20M rated at 10 Amps what size cable they uses?.
    Yes I need a lead a 0.5M longer and I want to buy the IEC plug itself and make my own lead using 1.5MM cable, I have a roll of 1.5MM cable, I have the 3 pin plug for the power Point but its not easy to buy The Rewireable IEC Female Plug. Ebay does not have them not unless you get them from the UK and it seems RS is the only other mob that stocks them.
    Any though where you can get them locally or even a Electrical wholesaler.
    Thanks



Look Here ->
  • #2
    Senior Member
    Reschs's Avatar
    Join Date
    Aug 2010
    Location
    Outside a few schooners
    Posts
    3,080
    Thanks
    908
    Thanked 2,147 Times in 1,058 Posts
    Rep Power
    933
    Reputation
    33238

    Default

    Altronics or Jaycar both sell them.
    Wagner Electronic Services ( WES) in Ashfield, Sydney.

  • #3
    Senior Member
    Reschs's Avatar
    Join Date
    Aug 2010
    Location
    Outside a few schooners
    Posts
    3,080
    Thanks
    908
    Thanked 2,147 Times in 1,058 Posts
    Rep Power
    933
    Reputation
    33238

    Default

    You could just buy a longer premade IEC Lead. They do come in various lengths.
    800 Watt is under 4 Amps, so a 10 Amp Lead is more than enough.

  • #4
    Premium Member
    Skepticist's Avatar
    Join Date
    Apr 2009
    Posts
    1,139
    Thanks
    714
    Thanked 670 Times in 525 Posts
    Rep Power
    475
    Reputation
    12780

    Default

    10A is the rated max current from a standard GPO IE 2.4kW.

  • #5
    Senior Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    4,271
    Thanks
    1,167
    Thanked 1,173 Times in 677 Posts
    Rep Power
    722
    Reputation
    21825

    Default

    Quote Originally Posted by Reschs View Post
    You could just buy a longer premade IEC Lead. They do come in various lengths.
    800 Watt is under 4 Amps, so a 10 Amp Lead is more than enough.
    Yes I look at a longer lead from ebay and I can cut off the 3 pin plug and shorten the lead and re plug it but thinking 1.0mm. Although its rated for 10 amps I always though that 1.5MM SQ is the smalless for 10AMP not 1.0MMSq

  • #6
    Senior Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    4,271
    Thanks
    1,167
    Thanked 1,173 Times in 677 Posts
    Rep Power
    722
    Reputation
    21825

    Default

    Quote Originally Posted by Skepticist View Post
    10A is the rated max current from a standard GPO IE 2.4kW.
    i'm talking about the IEC Plug that they Call KETTLE lead.. Me thinks that 1.0MM is too small

  • #7
    Senior Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    4,271
    Thanks
    1,167
    Thanked 1,173 Times in 677 Posts
    Rep Power
    722
    Reputation
    21825

    Default

    Quote Originally Posted by Reschs View Post
    Altronics or Jaycar both sell them.
    Wagner Electronic Services ( WES) in Ashfield, Sydney.
    I look at Jaycar on the net and they sell the IEC Male plug not the female one. Could have possible missed it.

  • #8
    Administrator
    mtv's Avatar
    Join Date
    Jan 2008
    Posts
    19,893
    Thanks
    7,508
    Thanked 15,066 Times in 6,761 Posts
    Rep Power
    5647
    Reputation
    239305

    Default

    Quote Originally Posted by Mr 672A View Post
    I look at Jaycar on the net and they sell the IEC Male plug not the female one. Could have possible missed it.



  • The Following User Says Thank You to mtv For This Useful Post:

    Mr 672A (12-03-18)

  • #9
    Senior Member
    loopyloo's Avatar
    Join Date
    Feb 2008
    Location
    Mid North Coast NSW . Australia
    Age
    67
    Posts
    2,207
    Thanks
    1,431
    Thanked 469 Times in 313 Posts
    Rep Power
    415
    Reputation
    7297

    Default

    That's kinda odd...Jaycar are calling them male plug and female socket, Should be female plug and male socket

  • #10
    Administrator
    mtv's Avatar
    Join Date
    Jan 2008
    Posts
    19,893
    Thanks
    7,508
    Thanked 15,066 Times in 6,761 Posts
    Rep Power
    5647
    Reputation
    239305

    Default

    Quote Originally Posted by loopyloo View Post
    That's kinda odd...Jaycar are calling them male plug and female socket, Should be female plug and male socket
    Any connector with pins is usually referred to as a plug and any connector with receptacles is usually referred to as a socket.

  • The Following 2 Users Say Thank You to mtv For This Useful Post:

    loopyloo (13-03-18),Mr 672A (12-03-18)

  • #11
    Senior Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    4,271
    Thanks
    1,167
    Thanked 1,173 Times in 677 Posts
    Rep Power
    722
    Reputation
    21825

    Smile

    Quote Originally Posted by mtv View Post
    Any connector with pins is usually referred to as a plug and any connector with receptacles is usually referred to as a socket.
    Thank you my Friend you are always on the Ball. I searched the Jaycar Thick and thin and I only found the Male one not the Female one and I need at Female one. For me Its confusing even more after the stroke so what I do now If it has something long coming out its a MALE and it it has a HOLE its a Female. (we heard that Before).
    On the UPS they dont recommend using extension leads from the Power point to the Original supplied Input lead with the IEC plug on the end of it and since most all IEC leads are 1.0MM it think its no good (maybe I'm paranoid the lead needs to be 2.5M long )Sq I want to make the exact distance from the PP to the UPS from 1.5 MM Sq cable which is a little thicker on the outside. I also have a full roll of 2.5MM 3 core Extension cable but the outside diameter is a lot thicker and it would be a pain for the male three pin plug and the IEC female on the other end.
    I will ring Jaycar and trott over there today if they have in in stock.

  • #12
    Senior Member
    Mr 672A's Avatar
    Join Date
    Jun 2012
    Location
    The only Country in the English speaking World where you cannot sue your Solicitor or Barrister.
    Posts
    4,271
    Thanks
    1,167
    Thanked 1,173 Times in 677 Posts
    Rep Power
    722
    Reputation
    21825

    Default

    Done with a 1.5 Lead. All good, thanks All

  • #13
    Premium Member
    Skepticist's Avatar
    Join Date
    Apr 2009
    Posts
    1,139
    Thanks
    714
    Thanked 670 Times in 525 Posts
    Rep Power
    475
    Reputation
    12780

    Default

    What I do when a custom length IEC power lead is required is get a cheap 10A extension lead that comes in 3, 5 or 10m lengths from the bargain store, lop off the standard in-line socket and fit the IEC plug. Quick and doesn't break the bank.