Thread: Brivis Buffalo 140 gas heater

  1. #1
    Premium Member

    Join Date
    Feb 2008
    Posts
    3,688
    Thanks
    1,938
    Thanked 2,104 Times in 1,050 Posts
    Rep Power
    968
    Reputation
    32468

    Default Brivis Buffalo 140 gas heater

    Can some one come up with a common sense answer re my heater. What happens is when it tries to come on in the morning it oscillates, going on and off. You have to switch it off, wait a while and retry, It eventually comes on. Once on all ok, the fan will switch on and off ok for the rest of the cycle, switch off and on again in the after noon with out a problem until it switches off at night, in the morning the problem resumes
    Got a Brivis (independent) heater technician in to look at it. He just scratched his head, but did not charge me
    Possible problem is an out of balance cylindrical fan putting pressure on the motor?
    Not game to touch the unit as the temp in Melbourne at the mo is around 12C thru the day and i don't think the boss would have (less) a sense of humor
    Thoughts boys
    P.S changed the control unit, but no difference
    Last edited by allover; 13-07-18 at 06:51 PM.
    There is a fine line between "Hobby" and "Madness"



Look Here ->
  • #2
    Administrator
    mtv's Avatar
    Join Date
    Jan 2008
    Posts
    19,908
    Thanks
    7,518
    Thanked 15,074 Times in 6,765 Posts
    Rep Power
    5651
    Reputation
    239465

    Default

    Did the tech check the gas pressure setting?

    Pressure can drop with temperature, so the morning cold start may be a result of insufficient pressure or a dodgy sensor.

  • #3
    Premium Member
    SS Dave's Avatar
    Join Date
    Feb 2010
    Location
    North Canberra
    Age
    63
    Posts
    2,124
    Thanks
    5,314
    Thanked 7,964 Times in 1,287 Posts
    Rep Power
    3355
    Reputation
    155622

    Default

    Quote Originally Posted by mtv View Post
    Did the tech check the gas pressure setting?

    Pressure can drop with temperature, so the morning cold start may be a result of insufficient pressure or a dodgy sensor.
    +1 for that!

    Years ago the gas ducted system would try and start 3 times then give up restarting it would work some times it had the techs stumped as what was wrong as when they rocked up to look in the arvo at it it would fire up first time. low pressure from the main regulator and dirty jets.

    SS Dave

  • #4
    Senior Member
    LeroyPatrol's Avatar
    Join Date
    Jan 2008
    Location
    N.E. Vic
    Posts
    16,229
    Thanks
    3,528
    Thanked 4,710 Times in 2,797 Posts
    Rep Power
    1670
    Reputation
    46551

    Default

    On a side note gas network company are offering nice incentives like $500 rebate on new heaters. I got a 5 star Braemer fully installed with 10 outlets for $3.5k. I remember installing myself a Mid efficiency Brivis unit 20 yrs ago and kit wasn't that much less!

    .....Leroy

  • #5
    Premium Member

    Join Date
    Feb 2008
    Posts
    3,688
    Thanks
    1,938
    Thanked 2,104 Times in 1,050 Posts
    Rep Power
    968
    Reputation
    32468

    Default

    Thanks guys, will start by cleaning the jets and ensure gas lines are not affected