    Default DGP not powering MAGLOCK

    Hi Guys

    Thanks in advance for helping out....

    I replaced an old faulty Maglock with a new one recently. The previous maglock was working fine except the contacts where worn out and grinding out the surface wont fix it.

    The new Maglock worked for about 20 mins and then lost power completely. At first glance i thought it was because of the batteries dc supply going into the 4DC but i checked and the battery was supplying its normal 12v to the dgp.

    One thing again was the SC reader lost power completely as well. Again i thought it was a faulty reader, i installed a new one still same problem. :confusion:

    Other doors on this 4DC are working fine except this one.

    I hope I explained this problem well enough



Look Here ->
  • #2
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    907
    Thanks
    156
    Thanked 146 Times in 133 Posts
    Rep Power
    276
    Reputation
    2409

    Default

    What fault finding have you done?

    Have you checked power at lock? Is new lock a higher current draw? Do you need to fit a diode across power?
    Swap it to a different door output for testing.

  • #3
    Junior Member
    Join Date
    Jan 2016
    Posts
    24
    Thanks
    1
    Thanked 2 Times in 2 Posts
    Rep Power
    101
    Reputation
    50

    Default

    Hi,

    A 4DC can only provide 250mA max power per relay & max Aux. 12VDC power is 700mA I believe. If you have maglock powered by the 4DC relay this is less than most single Maglocks require, a Lockwood Z4 is specified at 450mA and this consider a slimline maglock. try powering the maglock separately and confirm the results and if it restores functionality to the problematic reader.

    If not swap the reader to a working reader port on the 4DC to see if the reader port is the issue.

  • #4
    Junior Member Poody's Avatar
    Join Date
    Jul 2010
    Location
    Auckland NZ
    Posts
    145
    Thanks
    0
    Thanked 19 Times in 18 Posts
    Rep Power
    179
    Reputation
    380

    Default

    Best practice is a separate PSU for locks with individually fused locks. Allow at least 500ma per lock.