Has been a while since I’ve done one.
From memory you need to configure the reader as RAS 1 if connecting to 4DC.
Does the reader show any reaction when you badge the cards?
I have a 4 door intelligent controller i'm trying to setup smart card prox reader to work with it, i have the the cards programme, but i cant get the four door controller to work with them, the prox reader have being setup with the config card
Look Here -> |
Has been a while since I’ve done one.
From memory you need to configure the reader as RAS 1 if connecting to 4DC.
Does the reader show any reaction when you badge the cards?
Last edited by jrtech; 18-06-19 at 09:29 PM.
You need to connect them to the sub lan on the Ctlr.
Make sure that you have a term link resistor fitted across Data + Data - at the reader and have the term link jumper on at the panel.
In the controller poll the Ras number
In the door programming the reader type needs to be Tecom ASC
Add the door to any door groups required.
Aspire to Inspire Before you Expire!!
How have you programmed the reader and the cards?
Is it a new reader?
Do you have the TS0870 programming Guide.
Aspire to Inspire Before you Expire!!
Is the 4 door controller a TS0867 or TS0866? Either/Either you will need Firmware Version R110613.801 or greater so maybe check your firmware version.