You have to program in a Relay Control Group to RAS2.
The Relay Control Group (RCG) will corresponded to a Relay Number:
RCG 1 - Relay 1
RCG 2 - Relay 9
RCG 3 - Relay 17
RCG 4 - Relay 25
RCG 5 - Relay 33
RCG 6 - Relay 41
I have single door controller connected to V8 Panel.
The RAS number is 2.
My question is what is the address of the relay on the RAS2.
I need to trigger the relay once the card is tapped on the card reader connected to RAS2.
Look Here -> |
You have to program in a Relay Control Group to RAS2.
The Relay Control Group (RCG) will corresponded to a Relay Number:
RCG 1 - Relay 1
RCG 2 - Relay 9
RCG 3 - Relay 17
RCG 4 - Relay 25
RCG 5 - Relay 33
RCG 6 - Relay 41
I always start the numbering at the top end with RCG 32 - Relay 249 and use the same Event flag number if required then work my way back.
Avoids any conflicts on a growing system.
Just my bit
Aspire to Inspire Before you Expire!!
Just as a reference if you have already sorted it. You don't need to specify a relay control group for the ras UNLESS you want to control the relay with logic or a time zone. Just enable ras 2 into your door group and enable it with a timezone (not the same as the timezone mentioned earlier) and it will just work.