Hills r8 issues with reed zones on 5,6,7
Morning all, hope everyone is well
You guys have been a big help to me in the past with a couple of alarms, hoping you can help again
I work in the electrical maintenance field for mainly rentals properties.
Im not an expert on security systems but i do know a little just to get me by as part my role is to get alarms going for tenants of my clients when moving into properties. I work on alot of different of brands and models, so it is a little hard for me to get familiar with specific panels, and sometimes it a year or so that i work on the same model/brand panel.
My brother just bought a property and it has a Hills R8.
Of course the agents didnt pass on the user codes, so i told my brother not to worry, ill reset the panel and we will program it to his needs
So ive done that, and have got pretty much everything working.
However i got stuck with zones 5, 6, 7 not working at all
Zone 5 laundry reed
Zone 6 sliding door reed (which im still yet to find where the reeds actually are)
Zone 7 Windows reed (must be done in series, because there is 3 i believe)
I realized a week later. zone doubling!
So i went back last night, turned zone doubling on via Feature 22 Segment 5 option 2, checked the zones for 5, 6, 7 They are set to 16 like all the PIRS except entry PIR
But zones 5, 6, 7 keep flashing continously on keypad
Any ideas?
Thankyou in advance
Charlie
-
If the zones a flashing they are unsealed, check that the magnets a there and line up with the reed switches.
Use a multimeter to check the resistance of the alarm pair at the panel end wires.
Junior Member
- Rep Power
- 0
- Reputation
- 50
Thankyou Secure,
I thought i done something wrong programming to be honost
Ill check the magnets in next couple days, and check the ohms on the cables for the 5 6 7 zones at panel.
From memory, the resistor would be at the reed/pir side?
Normally at the reed / pir end.
Otherwise it could be in the panel where it connects to the main board if it was done by a lazy installer. Not good practice.
The Following User Says Thank You to secure For This Useful Post:
Junior Member
- Rep Power
- 0
- Reputation
- 50
Hi Secure,
i went back to my brothers, and opened up the panel,
Found 2 wires on zone 1 (which on doubling is zone 5) , but only 1 wire on zone 2,3,4 (zone doubling = 6, 7, 8)
Which means that the keypad was labelled incorrect.
Looks like there is no sliding door reeds, and the windows and laundry reeds are all connected in series on zone 5
I reprogrammed zone 6 and 7 to disabled
I checked the windows the magnet was missing on 2 of thew windows, so i put a magnet on both of them, and sure enough zone 5 stopped flashing
Thanks very much for your help with this, much appreciated
Also there was no resistors at the panel, except for zone 5 (which is the reed switches), so looks like the installer wasnt too bad in that case.
However, may i ask for my own knowledge why its better practice to have the resistors at the PIR side. Is this so you can also wire in the tamper on a pir still with 4core ( blue, white, + red - black)
Thanks for your time again secure, been a great help now and in the past
The Following User Says Thank You to horze For This Useful Post:
Best for resistor to be at sensor end to be more effective. Not just because of tamper. The resistor is also protecting the cable for shorts / open circuits.
I can understand why resistor was put in panel on zone 5 for easy fault finding otherwise you would need to pull apart each sensor to check which had the resistor.
Junior Member
- Rep Power
- 0
- Reputation
- 50
Junior Member
- Rep Power
- 0
- Reputation
- 50
Thanks secure, ill wire them up the way u recommended
After thinking about it, i finally understand the diagram with the 2 resistors. With the 2 resistors, its making the tamper a different zone by using the same cable as the resistor ratings being different would make 2 zones per PIR, Which means you will chew up alot of zones by doing it that way. 6 pirs would become 12 zones! There is a benefit in that way, cause you could have the tamper on 24h zone. But i think in domestic situation its not needed. With the 2 resistors/zones, it must be more for a commercial situation, so the tamper is on during the day when unarmed but the pir wouldnt be
thanks again for your help secure