    Default safety switch requirement

    Hi a questiop for all those sparkies out there. I am currently considering replacing my gas hot water system with an electric storage system. I have been shopping around and I am getting conflicting information. My question is "Should a storage Hot Water Service use a safety switch in the switchboard". My quotes are quite different with and without the safety switch. thank you.
    Last edited by gordonwh40; 22-11-20 at 05:59 AM.



Look Here ->
  • #2
    Senior Member
    fandtm666's Avatar
    Join Date
    Jan 2008
    Posts
    5,502
    Thanks
    244
    Thanked 990 Times in 465 Posts
    Rep Power
    1189
    Reputation
    40447

    Default

    Quote Originally Posted by gordonwh40 View Post
    "Should a storage Hot Water Service use a safety switch in the switchboard".
    Yes on a dedicated single circuit to the heater

  • #3
    Premium Member
    wotnot's Avatar
    Join Date
    Nov 2019
    Location
    Scenic Rim, SE Qld
    Posts
    3,236
    Thanks
    1,462
    Thanked 2,934 Times in 1,510 Posts
    Rep Power
    1334
    Reputation
    58690

    Default

    As of January 1 2019, the new AS3000 comes into effect and among numerous changes, how we (and you) treat hot water circuits from now on is one of them.
    If a hot water system is:

    • replaced and it had to be relocated in any way
    • replaced and the heating element in the new tank is larger than the original (eg. 2.4 k/w to a 3.6 k/w)
    • installed with a new circuit

    A safety switch, NOT just a circuit breaker is now required to protect the circuit AND an isolator must be installed within “arms reach” of the hot water system.

  • The Following 2 Users Say Thank You to wotnot For This Useful Post:

    gulliver (22-11-20),VroomVroom (23-11-20)

  • #4
    Premium Member
    gulliver's Avatar
    Join Date
    Jan 2008
    Location
    Sydney
    Age
    78
    Posts
    1,183
    Thanks
    10,878
    Thanked 341 Times in 234 Posts
    Rep Power
    337
    Reputation
    5032

    Default

    Does that mean replacing a HWS in the same place with an identical one you don't need the RCD?

  • #5
    Senior Member
    fandtm666's Avatar
    Join Date
    Jan 2008
    Posts
    5,502
    Thanks
    244
    Thanked 990 Times in 465 Posts
    Rep Power
    1189
    Reputation
    40447

    Default

    Quote Originally Posted by gulliver View Post
    Does that mean replacing a HWS in the same place with an identical one you don't need the RCD?
    yep

  • The Following User Says Thank You to fandtm666 For This Useful Post:

    gulliver (23-11-20)

  • #6
    Senior Member
    Guiseppe's Avatar
    Join Date
    May 2010
    Posts
    1,604
    Thanks
    1,057
    Thanked 413 Times in 279 Posts
    Rep Power
    366
    Reputation
    7224

    Default

    Quote Originally Posted by wotnot View Post
    AND an isolator must be installed within “arms reach” of the hot water system.
    An interesting requirement - our hot water system is under the house and definitely not easy to get at.

    One has to ask, " How qualified/experienced in the appropriate field are the people that prepare "our" standards?"
    If Australia is a democracy why, then, is voting compulsory?

    "What has changed between the arrival of the First Fleet and today?"
    "Wearing leg irons is now not required."

  • The Following 2 Users Say Thank You to Guiseppe For This Useful Post:

    gulliver (23-11-20),Uncle Fester (22-11-20)

  • #7
    Premium Member
    wotnot's Avatar
    Join Date
    Nov 2019
    Location
    Scenic Rim, SE Qld
    Posts
    3,236
    Thanks
    1,462
    Thanked 2,934 Times in 1,510 Posts
    Rep Power
    1334
    Reputation
    58690

    Default



    That just lists the latest changes in effect, you'd need look at previous incantations to get all the HWS history ; they hang heavily of the words 'new installation' ; old, existing installations may be another matter ; I'd imagine they rely on the fact a HWS will eventually fail, and if you have to fit a new unit you're subject to the latest wiring rules. Basically they're now treating the HWS wiring, in the same way the rules are for the electric oven/stove.

  • #8
    Senior Member

    Join Date
    Jul 2010
    Posts
    2,235
    Thanks
    2,822
    Thanked 1,514 Times in 835 Posts
    Rep Power
    795
    Reputation
    27703

    Default

    Quote Originally Posted by wotnot View Post
    I'd imagine they rely on the fact a HWS will eventually fail, and if you have to fit a new unit you're subject to the latest wiring rules. Basically they're now treating the HWS wiring, in the same way the rules are for the electric oven/stove.
    we had a whole new kitchen installed last year , with all new appliances in the same places , and no changes were made to any wiring , except the old wall oven was hard wired in , and the new wall oven now plugs into a 10A single power point in the cabinet .

  • #9
    Banned
    Join Date
    Aug 2008
    Location
    https://t.me/pump_upp
    Posts
    82
    Thanks
    206
    Thanked 30 Times in 19 Posts
    Rep Power
    0
    Reputation
    520

    Default

    Thank you all for that information. I will ensure the electrician who fits the heater fits a safety switch.