    Default DSC alarm and Smoke detector always open circuit

    I have a DSC alarm panel and a System Sensor 2012/24AUS smoke detector.

    Have wired 12V power
    Then the NC and C Relay connections back to my panel (together with resistor).

    My panel keeps showing an open circuit for my smoke detectors.

    I have one smoke that is daisy chained and have the same result.

    I am using the DLS software to program.

    Pls assist.
    Thanks



Look Here ->
  • #2
    Junior Member
    Join Date
    Feb 2018
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    Oh yes and one detectors LED is always green

  • #3
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    907
    Thanks
    156
    Thanked 146 Times in 133 Posts
    Rep Power
    276
    Reputation
    2409

    Default

    What fault finding have you done?
    Measure resistance on cable with multimeter?
    Put resistor straight across zone input to confirm fault clears etc?

  • #4
    Junior Member
    Join Date
    Dec 2020
    Posts
    2
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    Agree... resistor across zone input in panel as well as across the end of line pair used for that zone..
    Check zone programming ... maybe set as swap seal or similar
    Check relay on detector with multimeter (make sure the detector is actually working)