Is it a new door controller?
If its a 4 door you need to program the site code into it.
And upload everything to the controller.
I have a v8 panel, have just wired in a Wiegand 26bit fingerprint scanner and can verify that its passing Wiegand data, as when I go to the Last Card Read I can see the user and site code sent by the scanner, If I change the site code, the new site code is send so I know its definitely sending the correct data.
Program the site code in 19 - 20, Site code 1 = 255
Last Card Read = User 3 Site Code 255
But when checking menu 5 - 2 I get Access Denied - Invalid Site Code.
Any ideas? The reader is connect to a smart door controller.
Thank you
Look Here -> |
Is it a new door controller?
If its a 4 door you need to program the site code into it.
And upload everything to the controller.
Have you assigned the door and the user to the same door group?
Did you put in the site code as “255” or “000255”?
The system only accepts 6-digit site codes in system options.
deanfourie (26-08-21)