    Default Handover zone not working as expected

    Hi Everyone.

    Ive recently finished installing my solution 3000 and everything is working great, with the exception of the entry hallway sensor.

    I have my front door set to Delay -1, and my entry hallway sensor set to "Handover". However when i come into the house, the alarm is triggered instantly by the entry hallway sensor. It doesnt appear to be adhering to the handover.

    I've been reading through ALink, and i can see an option in there relating to "Handover Delay in Order". SOmething tells me this may have something to do with it but im not sure.

    My Entry hallway sensor is Zone 1, and my front door sensor (reed) is Zone 9. Technically this is not "in order" so im wondering if this is playing a role.

    Any guidance or advice much appreciated. Im losing browny points with my wife daily!.

    Dave



Look Here ->
  • #2
    Premium Member
    wotnot's Avatar
    Join Date
    Nov 2019
    Location
    Scenic Rim, SE Qld
    Posts
    3,236
    Thanks
    1,462
    Thanked 2,934 Times in 1,510 Posts
    Rep Power
    1334
    Reputation
    58690

    Default


  • #3
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    907
    Thanks
    156
    Thanked 146 Times in 133 Posts
    Rep Power
    276
    Reputation
    2409

    Default

    Yes you need to turn off the handover order feature. Handover Delay to be Sequential. Loc 494 less 8. So depending on other features you have enabled loc 494 less 8 so might be 0 if no other features used.