    Hi All

    as part of some work that is being done at my house there is a car hoist being installed.

    I have been in touch with the car hoist mob and they have indicated that they want the shed wired up first. unfortunately in order to do this the bank needs to release the funds however to release the funds they have indicated they need to perform an inspection the property and sight the hoist along with the other components on the renovation to be present.

    I have asked the hoist company if they will please do their calibration with power supplied using a 15 amp power extension lead connected to a 15 amp outlet on the side of the house and they have indicated that the resistance of the lead will cause start up capacitors to fail.

    This sounds like bs to me. if a cable is rated to 15 amps that is its rating.

    Can anyone confirm?



Look Here ->
  • #2
    Premium Member
    wotnot's Avatar
    Join Date
    Nov 2019
    Posts
    2,354
    Thanks
    1,031
    Thanked 2,128 Times in 1,117 Posts
    Rep Power
    961
    Reputation
    42570

    Default

    Depends on brand/model of hoist. the starting/working current requirement, type of motor/control used and length of wire run ~ it's not necessarily BS ...ie; many single phase hoists are rated around the 2.2kw -working- power, but initially at startup they can consume 3kw+....which is why they stipulate a 20amp supply circuit...(and this gets trickier if it's an inverter controlled motor...like our bore pump)

  • #3
    Senior Member
    freakee1's Avatar
    Join Date
    Jan 2008
    Location
    somewhere warmer
    Posts
    1,412
    Thanks
    207
    Thanked 730 Times in 390 Posts
    Rep Power
    393
    Reputation
    8454

    Default

    Single phase motors use capacitors to change the phase angle of the current during the moment of starting, hence creating the magnetic field which gets the motor moving.

    If they are not happy with a standard 15A lead (which is 1.5mm2) and high starting currents can cause a significant voltage drop. I would ask the hoist company if a 4mm2 lead would be suffice (this is good for 30A) and head off to Middy's or another Electrical Wholesalers and purchase the right length and get them to wire it in or create a super lead for your purposes.

    Caps typically won't fail - and are rated to handle large variances in voltages, but it can put the winding during the starting under duress momentarily.

    goodluck

    f
    Last edited by freakee1; 10-05-22 at 02:41 PM.
    有段者

  • #4
    Senior Member

    Join Date
    Jul 2010
    Posts
    2,189
    Thanks
    2,746
    Thanked 1,435 Times in 800 Posts
    Rep Power
    740
    Reputation
    26123

    Default

    Sounds like BS to me ,
    a sparkie will not install a fixed line to a hoist until the hoist is installed. Hence why hoist installers set up and commission the unit on fly leads off an extension cord

  • #5
    Premium Member RedXT's Avatar
    Join Date
    Mar 2008
    Posts
    561
    Thanks
    347
    Thanked 165 Times in 89 Posts
    Rep Power
    248
    Reputation
    2784

    Default

    Quote Originally Posted by VroomVroom View Post
    Sounds like BS to me ,
    a sparkie will not install a fixed line to a hoist until the hoist is installed. Hence why hoist installers set up and commission the unit on fly leads off an extension cord
    Yea I have had 2 hoists installed in the past 5 years and know of 3 others and the installers had no problems commissioning them with a fly lead and extension cord

  • #6
    Senior Member
    Uncle Fester's Avatar
    Join Date
    Jan 2008
    Location
    Commonly found in a pantry or the bottom of a fridge, searching for grains, fermented or distilled
    Posts
    6,088
    Thanks
    2,172
    Thanked 4,183 Times in 2,389 Posts
    Rep Power
    1921
    Reputation
    77158

    Default

    Quote Originally Posted by wotnot View Post
    Depends on brand/model of hoist. the starting/working current requirement, type of motor/control used and length of wire run ~ it's not necessarily BS ...ie; many single phase hoists are rated around the 2.2kw -working- power, but initially at startup they can consume 3kw+....which is why they stipulate a 20amp supply circuit...(and this gets trickier if it's an inverter controlled motor...like our bore pump)
    I am on the B.S. side too, unless you intend to use a 30m extension or more.

    240V x 15A = 3.6kW, that should be sufficient to start up a 2.2kW motor.

    If a 1.5mm^2, 10m extension is used then you would have a voltage drop of about 3.5V at 15A.

    The Australian Standard mains voltage limits are from 216V to 253V, so your hoist must be able to perform in that voltage range.

    Assuming you measure at the time of the test a typical 235V unloaded, then a momentary voltage drop of 3.5V is well within those limits. Even 20A with 4.7V drop not a problem.
    I would place the limit at 20m and 20A, which is about 9,5V voltage drop.
    I am an arrogant, irritating RSole.