    Default S2001 Rate of Rise Detector

    Hi guys

    Just wanted some input on these detectors. There is no paperwork ever supplied with them and I've tried various wiring configurations and it doesn't work as I imagine it should

    I can get one to work if I don't use any EOL resistors. But, as soon as I add a single EOL it seals ok but shorts on alarm. I've tried various different connections and found documentation online but still doesn't work.

    Heres my simple wiring for Single EOL (which doesn't work)

    Im using a 4 core but only two wires needed I believe

    So, white cable to terminal L1
    Resistor from L2 to C2
    Blue cable to terminal C1

    Using a Bosch 6000, so I can see that when I have the detector part connected, it is showing 3351 ohms (corrrect, as I am using 3K3)
    When I remove the base I get 55068 ohms
    When fitted and using a hair dryer to test, the red light illuminates and shows a short on the codepad and 611 ohms

    Ideas?

    Cheers



Look Here ->
  • #2
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    907
    Thanks
    156
    Thanked 146 Times in 133 Posts
    Rep Power
    276
    Reputation
    2409

    Default

    and click on data sheet.

    When it shorts (Alarm) doesn't the zone go into alarm? Just can not use the opposite 6K8 zone.

    Or look at trying the invert seal option in zone programming.

  • #3
    Junior Member
    Join Date
    May 2019
    Location
    Brisbane
    Posts
    45
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Rep Power
    62
    Reputation
    70

    Default

    Hi there

    Yes, it can be used with short, but I was just wondering if there was another way. The main problem is using DEOL. Challenger is ok because it sees 20K or 5K as alarm and copes with this quite well. The problem is with DEOL 6k8/3K3, or Concept 2K2/6K8. I havent found a workaround for these configs yet.

    Thanks for your reply