    Wink c&k 238i

    hi guys just need some help with my c&k 238i i had to reprogram the dialler to ring my mobile phone it rings my mobile and makes a alarm sound but when i get home the trouble light is on i have turned off the event reporting and and opening and closeing reports so i dont know if i have stuffed up in command location 0A or what so dos anyone have an idea whats going on.



Look Here ->
  • #2
    Senior Member
    Join Date
    Jan 2008
    Posts
    503
    Thanks
    92
    Thanked 50 Times in 37 Posts
    Rep Power
    219
    Reputation
    293

    Default

    If you are setting up for mobile phone dialling you would only activate
    in each loop programming enable Alarm reporting no restore or shunting ,
    location 2A 2B 2C disable everything
    and select personal dialling in OA
    Normally when panels are set up for personal dial they are not looking for a kiss off from the control room receiver so after making the call should be okay.
    Have you setup panel for personal dialling if not panel every time it dial control room will send its data then wait for kiss off before hanging up
    after the number of dial attempts and no kiss off you would get a trouble light