    Default 240 Volt Plug getting hot

    I got a fan heater - 2000 Watts

    I run it in the bathroom and after maybe 15 minutes the Plug got stinkin' hot.
    I figured there must be a poor connection so I cut off the molded-on plug and put on another one.

    This one is getting hot too.
    The heat appears to be starting from the Active Pin.

    The screws holding the wires are tight, and the outlet seems to be fine.
    This new plug is made of soft plastic, and the pin sort of melted the plastic.
    VERY HOT.

    I figure there must be poor electrical contact between the pin and the outlet.
    The neutral pin doesn't even get warm.

    I ain't tried it yet, but I'm considering plugging the heater into another room outlet to see if it still gets the plug stinkin' hot.

    Could someone fill me in as to whats going on here before I burn me house down?



Look Here ->
  • #2
    Senior Member
    beer4life's Avatar
    Join Date
    Feb 2008
    Location
    The Nether World.
    Age
    90
    Posts
    6,375
    Thanks
    1,351
    Thanked 1,452 Times in 1,066 Posts
    Rep Power
    560
    Reputation
    7552

    Wink

    Quote Originally Posted by moeee View Post
    I got a fan heater - 2000 Watts

    I run it in the bathroom and after maybe 15 minutes the Plug got stinkin' hot.
    I figured there must be a poor connection so I cut off the molded-on plug and put on another one.

    This one is getting hot too.
    The heat appears to be starting from the Active Pin.

    The screws holding the wires are tight, and the outlet seems to be fine.
    This new plug is made of soft plastic, and the pin sort of melted the plastic.
    VERY HOT.

    I figure there must be poor electrical contact between the pin and the outlet.
    The neutral pin doesn't even get warm.

    I ain't tried it yet, but I'm considering plugging the heater into another room outlet to see if it still gets the plug stinkin' hot.

    Could someone fill me in as to whats going on here before I burn me house down?
    You need to replace your outlet socket/wall plate.

  • #3
    Senior Member omega99's Avatar
    Join Date
    Feb 2008
    Posts
    624
    Thanks
    53
    Thanked 55 Times in 40 Posts
    Rep Power
    225
    Reputation
    358

    Default

    ditto replace the power outlet
    woteva

  • #4
    Senior Member Moof's Avatar
    Join Date
    Jan 2008
    Location
    Geelong, Victoria
    Age
    50
    Posts
    520
    Thanks
    48
    Thanked 62 Times in 33 Posts
    Rep Power
    221
    Reputation
    292

    Default

    Get a licenced electrician to replace your socket outlet on the wall

  • #5
    Banned
    Join Date
    Jan 2008
    Posts
    1,101
    Thanks
    180
    Thanked 92 Times in 65 Posts
    Rep Power
    0
    Reputation
    -336

    Default

    Quote Originally Posted by Moof View Post
    Get a licenced electrician to replace your socket outlet on the wall
    I'ld rather live a little on the wild side and attempt the replacement myself.

    Obviously it couldn't be too difficult or surely the replacements wouldn't be so generally available to purchase.

    But the main reason I'ld prefer to do it is because the prices these licensed electricians would charge me would be unviable.

    Too much red tape and beaurocratic bullshit in this world already without having me add further to it.

    And laziness.

    I mean - how hard could it be?

  • #6
    Senior Member
    best4less's Avatar
    Join Date
    Jan 2008
    Location
    Australia
    Posts
    7,684
    Thanks
    3,487
    Thanked 2,207 Times in 1,132 Posts
    Rep Power
    758
    Reputation
    15165

    Default

    DxE=C+(y+z)=W\X+F=







    Lets see

    X= fee for electrician
    Y=total cost of house (including burnt rubbish removal)
    Z=price of land
    W=total land and house cost
    C=cost of human life
    D=average working years of a Human
    E=average yearly wage
    F=the cost to get your IQ tested
    When you do things right, people won't be sure that you have done anything at all

  • The Following 4 Users Say Thank You to best4less For This Useful Post:

    bss904 (04-09-09),iwacelect (04-09-09),omega99 (10-09-09),Oscar (10-09-09)

  • #7
    Senior Member
    beer4life's Avatar
    Join Date
    Feb 2008
    Location
    The Nether World.
    Age
    90
    Posts
    6,375
    Thanks
    1,351
    Thanked 1,452 Times in 1,066 Posts
    Rep Power
    560
    Reputation
    7552

    Wink

    Quote Originally Posted by moeee View Post
    I'ld rather live a little on the wild side and attempt the replacement myself.

    Obviously it couldn't be too difficult or surely the replacements wouldn't be so generally available to purchase.
    Quote Originally Posted by moeee View Post

    But the main reason I'ld prefer to do it is because the prices these licensed electricians would charge me would be unviable.

    Too much red tape and beaurocratic bullshit in this world already without having me add further to it.

    And laziness.

    I mean - how hard could it be?
    If you don't know what you're doing, Fatal.
    Last edited by beer4life; 04-09-09 at 08:57 AM.

  • #8
    Senior Member
    iwacelect's Avatar
    Join Date
    Jan 2008
    Posts
    2,581
    Thanks
    858
    Thanked 663 Times in 434 Posts
    Rep Power
    368
    Reputation
    4190

    Default

    Quote Originally Posted by best4less View Post
    DxE=C+(y+z)=WX+F=







    Lets see

    X= fee for electrician
    Y=total cost of house (including burnt rubbish removal)
    Z=price of land
    W=total land and house cost
    C=cost of human life
    D=average working years of a Human
    E=average yearly wage
    F=the cost to get your IQ tested
    thats priceless B4L, well done, oh and he'd better get f'd real sooooon!
    Last edited by iwacelect; 04-09-09 at 09:52 AM.
    When I explained to the guy what avatar I wanted, that wasn't what I meant!

  • #9
    Senior Member
    LeroyPatrol's Avatar
    Join Date
    Jan 2008
    Location
    N.E. Vic
    Posts
    16,229
    Thanks
    3,528
    Thanked 4,710 Times in 2,797 Posts
    Rep Power
    1670
    Reputation
    46551

    Default

    Quote Originally Posted by beer4life View Post
    [CENTER]

    If you don't know what you're doing, Fatal.
    especially if the red and the black or was it the blue and the brown or the brown and the black.....gee which wire went where?
    We can see the next post after it's changed, whay does my heater zap me when I plug it in?

    Cheers,
    Leroy
    XCRUISER HDSR600HD twin sat and terrestrial receiver $OOS *
    XCRUISER HDSR385 Avant - sold out$OOS UltraPlus DVB-T and DVB-S2 tuners $49 Remotes $OOS

  • #10
    Banned
    Join Date
    Jan 2008
    Posts
    1,101
    Thanks
    180
    Thanked 92 Times in 65 Posts
    Rep Power
    0
    Reputation
    -336

    Default

    I figure an IQ of 126 should be capable of replacing the GPO.

    And I also figure that 8 years of experience repairing television and other electronic equipment should also qualify as to capable.

    I figure if you shove that into your Formula, it pretty much cancels out both sides to give me a fair chance of getting it right.

    Thanks for your concerns about my welfare anyway.
    Was more concerned about why the plug was getting hot.

    Just shows why the world initiates Pagan Rites to celebrate the birth of the Messiah.

  • #11
    Senior Member
    LeroyPatrol's Avatar
    Join Date
    Jan 2008
    Location
    N.E. Vic
    Posts
    16,229
    Thanks
    3,528
    Thanked 4,710 Times in 2,797 Posts
    Rep Power
    1670
    Reputation
    46551

    Default

    Quote Originally Posted by moeee View Post
    And I also figure that 8 years of experience repairing television and other electronic equipment should also qualify as to capable.
    Now we're all wondering why you asked why it's getting hot :P

    Leroy
    XCRUISER HDSR600HD twin sat and terrestrial receiver $OOS *
    XCRUISER HDSR385 Avant - sold out$OOS UltraPlus DVB-T and DVB-S2 tuners $49 Remotes $OOS

  • The Following 3 Users Say Thank You to LeroyPatrol For This Useful Post:

    bss904 (04-09-09),Godzilla (04-09-09),weirdo (04-09-09)

  • #12
    Senior Member
    iwacelect's Avatar
    Join Date
    Jan 2008
    Posts
    2,581
    Thanks
    858
    Thanked 663 Times in 434 Posts
    Rep Power
    368
    Reputation
    4190

    Default

    Quote Originally Posted by LeroyPatrol View Post
    Now we're all wondering why you asked why it's getting hot :P

    Leroy
    exactly!
    When I explained to the guy what avatar I wanted, that wasn't what I meant!

  • #13
    Senior Member
    best4less's Avatar
    Join Date
    Jan 2008
    Location
    Australia
    Posts
    7,684
    Thanks
    3,487
    Thanked 2,207 Times in 1,132 Posts
    Rep Power
    758
    Reputation
    15165

    Default

    Quote Originally Posted by moeee View Post

    Just shows why the world initiates Pagan Rites to celebrate the birth of the Messiah.
    The Price of eggs in Russia are going up this morning

    But serious it's all in the house insurance that causes the people that know what their doing not to do it that's all we are not covered plain and simple And you right about me Equation i left out the

    G= fun
    J= Tongue and Cheek
    L= No harm no foul

    When you do things right, people won't be sure that you have done anything at all

  • The Following User Says Thank You to best4less For This Useful Post:

    Godzilla (04-09-09)

  • #14
    Banned
    Join Date
    Jan 2008
    Posts
    1,101
    Thanks
    180
    Thanked 92 Times in 65 Posts
    Rep Power
    0
    Reputation
    -336

    Default

    Quote Originally Posted by LeroyPatrol View Post
    Now we're all wondering why you asked why it's getting hot :P

    Leroy
    So all those capacitors with Low ESR you replaced over the years, any idea why the ESR was low?

    Would it enable the repair to be any different having known?

    I am technician, not an engineer.
    I can put things right, but it don't necessarily follow that I need to know why things are as they are.

    Sometimes that metal thing with iron on the end is known as a hammer.
    Regardless of its name , it still belts them nails in just the same.

    When I replace parts, I prefer to know why the original failed because that becomes knowledge, which improves ability.

  • #15
    Senior Member
    iwacelect's Avatar
    Join Date
    Jan 2008
    Posts
    2,581
    Thanks
    858
    Thanked 663 Times in 434 Posts
    Rep Power
    368
    Reputation
    4190

    Default

    Quote Originally Posted by moeee View Post
    So all those capacitors with Low ESR you replaced over the years, any idea why the ESR was low?

    Would it enable the repair to be any different having known?

    I am technician, not an engineer.
    I can put things right, but it don't necessarily follow that I need to know why things are as they are.

    Sometimes that metal thing with iron on the end is known as a hammer.
    Regardless of its name , it still belts them nails in just the same.

    When I replace parts, I prefer to know why the original failed because that becomes knowledge, which improves ability.
    please stop....my sides hurt.....no more...please stop......
    When I explained to the guy what avatar I wanted, that wasn't what I meant!

  • #16
    Junior Member
    Join Date
    Aug 2009
    Location
    Western Australia
    Posts
    147
    Thanks
    16
    Thanked 11 Times in 7 Posts
    Rep Power
    184
    Reputation
    47

    Default

    Wouldnt most Technicians have a Plug and Socket License? Surely this would be enough to be capable of removing a wall socket (switch off mains supply) remove three wires, fit socket and test that it is correctly wired. Bunnings have a nice little 3 pin plug with neons that indicate if wiring is correct or faulty.

  • #17
    Premium Member
    gulliver's Avatar
    Join Date
    Jan 2008
    Location
    Sydney
    Age
    78
    Posts
    1,183
    Thanks
    10,927
    Thanked 341 Times in 234 Posts
    Rep Power
    338
    Reputation
    5032

    Default

    And the plug should also be replaced as it will damage the new powerpoint again.

  • #18
    Senior Member Mgoldbe1's Avatar
    Join Date
    Jan 2009
    Location
    Geelong, Vic.
    Posts
    682
    Thanks
    367
    Thanked 265 Times in 150 Posts
    Rep Power
    235
    Reputation
    1396

    Default

    How hard could it be??....it's only 3 wires...and only 2 do anything....

    Hope you have an RCD in your switchboard just incase...

  • #19
    Senior Member
    best4less's Avatar
    Join Date
    Jan 2008
    Location
    Australia
    Posts
    7,684
    Thanks
    3,487
    Thanked 2,207 Times in 1,132 Posts
    Rep Power
    758
    Reputation
    15165

    Default

    And here i am thinking it only takes one wire to kill you, I am laughing now
    When you do things right, people won't be sure that you have done anything at all

  • #20
    Senior Member
    iwacelect's Avatar
    Join Date
    Jan 2008
    Posts
    2,581
    Thanks
    858
    Thanked 663 Times in 434 Posts
    Rep Power
    368
    Reputation
    4190

    Default

    Quote Originally Posted by Mgoldbe1 View Post
    How hard could it be??....it's only 3 wires...and only 2 do anything....

    Hope you have an RCD in your switchboard just incase...
    only 2 do anything????????????????

    I'm glad your not going anywhere near me with that knowledge

    what do they say "a little knowledge is a dangerous thing"
    When I explained to the guy what avatar I wanted, that wasn't what I meant!

  • Page 1 of 6 123456 LastLast

    Similar Threads

    1. 12 Volt decoders?
      By Flippy in forum Decoders
      Replies: 7
      Last Post: 26-06-09, 06:15 PM
    2. 12 volt relays
      By Keith in forum Buy Sell and Trade
      Replies: 2
      Last Post: 17-01-09, 06:20 PM
    3. How to use a Volt Meter
      By Paulypudding in forum Electronics
      Replies: 14
      Last Post: 30-09-08, 02:22 PM
    4. ###?????What Plug Is This??????####
      By urban_s0ulja in forum Electronics
      Replies: 19
      Last Post: 16-07-08, 05:33 PM
    5. 9 volt battery fooled IQ box
      By slothslag in forum Satellite TV General
      Replies: 5
      Last Post: 18-04-08, 11:57 PM

    Bookmarks

    Posting Permissions

    • You may not post new threads
    • You may not post replies
    • You may not post attachments
    • You may not edit your posts
    •