    Default Challenger + 4 Door Controller Issue

    Good Afternoon All,

    I have a Tecom Challenger V8 with 4 Door controller installed in a building. I am having issues with the system reading from the users database.

    Whenever a user swipes it comes up as invalid user. I have triple checked the site code (no offset), user is definitely active in the dbase and has correct door group etc assigned.

    Any ideas?



Look Here ->
  • #2
    Junior Member
    Join Date
    Nov 2009
    Location
    Sydney Metro, NSW
    Posts
    205
    Thanks
    121
    Thanked 34 Times in 31 Posts
    Rep Power
    186
    Reputation
    240

    Default

    What is the exact error in the event log... is it invalid user or something else?

    If so then check what type the Door Controller is in the DGP database - if not door controller then no users are passed from the challenger to the 4DC...

    If Access denied void door = door group issue - i.e. door group not in challenger - older versions of TITAN had issues downloading the door groups...

  • #3
    Junior Member
    Join Date
    Sep 2010
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    The door controller is listed in the dbase. (I am using Titan software FYI).

    Our regional tech was able to sort the issue out by shorting both panels.

  • #4
    Junior Member
    Join Date
    May 2010
    Posts
    111
    Thanks
    33
    Thanked 9 Times in 9 Posts
    Rep Power
    174
    Reputation
    55

    Default

    Check the user through the RAS, see if the door group is correct.

  • #5
    Senior Member
    intelliGEORGE's Avatar
    Join Date
    Jan 2008
    Location
    Sydney, AUSTRALIA
    Age
    43
    Posts
    4,106
    Thanks
    884
    Thanked 1,484 Times in 691 Posts
    Rep Power
    479
    Reputation
    7236

    Default

    With 4 door controllers you need to default them in order for them to pull down the DB from the challenger. Especially if it is a new install.

  • #6
    Junior Member
    Join Date
    Jul 2009
    Posts
    10
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Rep Power
    0
    Reputation
    30

    Default

    1. Have card users ever worked or just stopped working ?

    2. Just a simple one, always check on a 4DC board that the "card swipe" jumper pin isn't on, that will mess with the panels card reads etc.

  • #7
    Junior Member Geek's Avatar
    Join Date
    Sep 2010
    Location
    Melbourne
    Posts
    33
    Thanks
    21
    Thanked 0 Times in 0 Posts
    Rep Power
    167
    Reputation
    10

    Post

    Just for the sake of recording my experience...

    Had the same issue...same symptoms
    Ultimately found prox card user number and tecom user number mismatch.

  • #8
    Member
    Join Date
    Jun 2011
    Posts
    483
    Thanks
    121
    Thanked 117 Times in 85 Posts
    Rep Power
    193
    Reputation
    1019

    Default

    Quote Originally Posted by paulc101 View Post
    Good Afternoon All,

    I have a Tecom Challenger V8 with 4 Door controller installed in a building. I am having issues with the system reading from the users database.

    Whenever a user swipes it comes up as invalid user. I have triple checked the site code (no offset), user is definitely active in the dbase and has correct door group etc assigned.

    Any ideas?
    Something that is often overlooked and quite simple questions but...

    what user numbers are you using? have you recently gone above 50 users? have you done a 1meg memory chip upgrade or are you still using standard memory?

    Are you checking Titan DB or actually at the RAS programming? as I'm sure you're well aware Titan will let you program user 51 as an active user but at the RAS you cant.

    One of my techs sat on a problem like this for nearly a week going through all these complicated possibilities but when I attended site to see what was taking so long the problem was sorted by a quick memory upgrade!

  • #9
    Member Security's Avatar
    Join Date
    May 2008
    Posts
    319
    Thanks
    51
    Thanked 73 Times in 55 Posts
    Rep Power
    212
    Reputation
    400

    Default

    Quote Originally Posted by intelliGEORGE View Post
    With 4 door controllers you need to default them in order for them to pull down the DB from the challenger. Especially if it is a new install.
    Just as intelliGEORGE has stated, I STRONGLY recommend this for all new PCBs. Sometimes tested products are not defaulted correctly before they are packed and shipped.

    Most of the time you probably won't need to do this but if it saves time on unnecessary fault finding...