    Default Solution 16 all zones shorted

    I have setup my first Solution 16 plus panel at home, when I go to Zone status all of my zones say EOL = Short.

    When I set the alarm it says that all zones are open and I have to hit okay to force arming, I am assuming that this relates to the EOL = Short

    I am wondering what I have done wrong to make all my zones shorted? Any help will be appreciated
    Last edited by hargy01; 20-07-11 at 08:18 PM. Reason: Update



Look Here ->
  • #2
    Senior Member
    intelliGEORGE's Avatar
    Join Date
    Jan 2008
    Location
    Sydney, AUSTRALIA
    Age
    43
    Posts
    4,106
    Thanks
    884
    Thanked 1,484 Times in 691 Posts
    Rep Power
    479
    Reputation
    7236

    Default

    Did you install EOL resistors in your devices (PIR's, Reed switches etc)?

  • #3
    Junior Member
    Join Date
    Jul 2011
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    I used EOL resistors in the alarm, didn't use them in the PIR's or reed switches.

    Just used the orange ones that came with the system which where 3k3 I think. Only have 6 zones, am I able to get rid of the resistors?
    Last edited by hargy01; 20-07-11 at 09:20 PM. Reason: spelling

  • #4
    Banned
    watchdog's Avatar
    Join Date
    Jan 2008
    Posts
    2,966
    Thanks
    136
    Thanked 869 Times in 514 Posts
    Rep Power
    0
    Reputation
    8320

    Cool

    Check that menu 340 is still set at 5
    Check that the EOL are wired in series & not across the zone I/P

    The EOL should be wired in the PIR not the panel
    I think you'll find the "orange" ones are the 6k8
    If you want to get rid of the resistors (not recommended) then menu 340 should be set to 0

  • #5
    Senior Member
    intelliGEORGE's Avatar
    Join Date
    Jan 2008
    Location
    Sydney, AUSTRALIA
    Age
    43
    Posts
    4,106
    Thanks
    884
    Thanked 1,484 Times in 691 Posts
    Rep Power
    479
    Reputation
    7236

    Default

    Quote Originally Posted by watchdog View Post
    I think you'll find the "orange" ones are the 6k8
    Are you sure? I thought they were 3K3 being the same color as the first band. I.e 3=Orange, 6=Blue

  • #6
    Senior Member secure's Avatar
    Join Date
    Jan 2008
    Location
    W.A
    Posts
    911
    Thanks
    157
    Thanked 147 Times in 134 Posts
    Rep Power
    277
    Reputation
    2429

    Default

    Quote Originally Posted by intelliGEORGE View Post
    Are you sure? I thought they were 3K3 being the same color as the first band. I.e 3=Orange, 6=Blue
    George is correct

  • #7
    Banned
    watchdog's Avatar
    Join Date
    Jan 2008
    Posts
    2,966
    Thanks
    136
    Thanked 869 Times in 514 Posts
    Rep Power
    0
    Reputation
    8320

    Cool

    You may be right. My eyes aren't good enough to read them anymore. Orange could be red. Blue could be grey. And the ink they use nowdays leaves a lot to be desired. I regularly check them with a MM & separate them into two containers.

  • #8
    Junior Member
    Join Date
    Jul 2011
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Rep Power
    0
    Reputation
    10

    Default

    OK so last night I removed the eol resistors from the panel and set menu 340 to 0. The alarm works properly.

    Why is not rcommended to install without EOL resistors?

    If I move the resistors to the end device and set menu 340 back to 5, should that work?

  • #9
    Banned
    watchdog's Avatar
    Join Date
    Jan 2008
    Posts
    2,966
    Thanks
    136
    Thanked 869 Times in 514 Posts
    Rep Power
    0
    Reputation
    8320

    Cool

    With no EOL any short circuit fault condition will not present as a fault. The panel cannot distinguish between a s/c on the cabling or a short cct from the relay in the pir.
    The resistor is normally placed in the pir & will provide supervision of the cabling integrity. As long as you wire them in the PIR correctly & change menu 340 to 5 then it will work.

  • #10
    Senior Member
    downunderdan's Avatar
    Join Date
    Sep 2008
    Location
    Sydney Metropolitan
    Posts
    2,497
    Thanks
    163
    Thanked 601 Times in 422 Posts
    Rep Power
    365
    Reputation
    4649

    Default

    Hargy01,

    I don't mean to discourage DIY or people trying to educate themselves. However the question you've asked demonstrates a lack of knowledge coupled with a failure to use Google when some things were pointed out.

    The reason I raise this, is I'm guessing you aren't installing the system on a workbench in your shed, for cheap thrills. Rather, I expect you're installing it in your home, where you expect it to protect your belongings, and quite possibly your safety.

    People here are usually happy to help those with genuine questions, or whose own research has led them up against a brick wall. However with respect, I don't think you're at that impasse yet and I believe you may be doing something with some significant negative consequences that you haven't fully considered.

  • #11
    Member
    Join Date
    Aug 2010
    Location
    NE Vic
    Age
    38
    Posts
    304
    Thanks
    27
    Thanked 27 Times in 23 Posts
    Rep Power
    180
    Reputation
    160

    Default

    Dan your such a sourpuss at times

  • The Following User Says Thank You to Uncle Kneebo For This Useful Post:

    downunderdan (22-07-11)

  • #12
    Member
    Join Date
    Oct 2010
    Posts
    339
    Thanks
    14
    Thanked 60 Times in 56 Posts
    Rep Power
    187
    Reputation
    644

    Default

    Quote Originally Posted by Uncle Kneebo View Post
    Dan your such a sourpuss at times
    A bit harsh. I don't always agree with everything Dan says, but in this case, when it comes to securing yourself and your property, he does have a point. Get a professional to do it properly.
    Last edited by alarmman; 21-07-11 at 07:31 PM.

  • #13
    Senior Member

    Join Date
    May 2010
    Posts
    2,106
    Thanks
    252
    Thanked 839 Times in 515 Posts
    Rep Power
    369
    Reputation
    6489

    Default

    Quote Originally Posted by hargy01 View Post

    Why is not rcommended to install without EOL resistors?
    Tell you what. You set it up without EOL, then PM me your address along with times the system's going to be armed. The purpose of EOLs will soon become apparent.

  • #14
    Member
    Join Date
    Aug 2010
    Location
    NE Vic
    Age
    38
    Posts
    304
    Thanks
    27
    Thanked 27 Times in 23 Posts
    Rep Power
    180
    Reputation
    160

    Default

    I was giggling as I typed it, its not all doom and gloom.
    Yeah but said installer takes the risk putting it in. Better than his sparky mate doing it and ####ing it up then pointing fingers....
    all about having a go

  • #15
    Junior Member
    Join Date
    Apr 2009
    Location
    Tauranga
    Posts
    145
    Thanks
    51
    Thanked 13 Times in 13 Posts
    Rep Power
    189
    Reputation
    120

    Default

    Quote Originally Posted by watchdog View Post
    You may be right. My eyes aren't good enough to read them anymore. Orange could be red. Blue could be grey. And the ink they use nowdays leaves a lot to be desired. I regularly check them with a MM & separate them into two containers.
    The resistors supplied are solid orange for 3k3 and solid blue for 6k8, just like paradox use green for 1k.

  • #16
    Banned
    watchdog's Avatar
    Join Date
    Jan 2008
    Posts
    2,966
    Thanks
    136
    Thanked 869 Times in 514 Posts
    Rep Power
    0
    Reputation
    8320

    Cool

    Quote Originally Posted by NZ Alarm Tech View Post
    The resistors supplied are solid orange for 3k3 and solid blue for 6k8, just like paradox use green for 1k.
    Well I can understand an orange body counting as 3k3 & a blue body counting as 6k8 - but a green body meaning 1K is just being stoopid