    Default Question about Instant gas hot water service

    I have a Bosch WR250-1B instant gas hot water service on my boat, The question I have is is it normal for the burner to continue burning for around 20 seconds after the water has turned off or should the flame go out as soon as the water is shut off. It has battery ignition.

    Any gas techs here Thanks



Look Here ->
  • #2
    Junior Member
    Join Date
    Jan 2010
    Posts
    154
    Thanks
    18
    Thanked 32 Times in 25 Posts
    Rep Power
    182
    Reputation
    152

    Default

    Try this link on instructions, not sure if it is exact same unit....


    20 seconds sounds too long as most hot water units switch off straight away or up to 5 seconds max.

  • The Following User Says Thank You to officemanager For This Useful Post:

    dungbeetle46 (27-06-12)

  • #3
    Member dungbeetle46's Avatar
    Join Date
    Jun 2008
    Location
    South Aus
    Age
    60
    Posts
    320
    Thanks
    138
    Thanked 273 Times in 69 Posts
    Rep Power
    231
    Reputation
    1458

    Default

    Thats definitely the unit, much appreciated

  • #4
    Premium Member

    Join Date
    Jan 2008
    Location
    Central Tablelands of NSW
    Age
    81
    Posts
    13,824
    Thanks
    1,242
    Thanked 3,806 Times in 2,525 Posts
    Rep Power
    1797
    Reputation
    56986

    Default

    I am not a tech but I would think being LPG, even tho the water/Gas tap are closed, there woulld be a few moments of Gas left in the pipe to burn.
    I have a RedRock brand unit and I take it yours turns ON (ignites) once the water volume passes a certain point then goes off as the water flow is turned Off.
    I must say I havent really 'Timed' it but I have the impression that as I turn the water off as quickly as I can, the flame goes out almost immediately the water flow has stopped.
    This unit has a loud distinct 'Click' when it starts and stops which I take is the water driven Gas control opening and closing the Gas valve.
    If your in any way worried, I would get it serviced as those units work great and are built with safety in mind but things can and do go wrong unfortunately with diasterous results.
    And being on a boat (salt or freshwater) would make me more cautious too.

    I have never seen inside of one or have a clue how the waterflow control works the Gas valve but if its mechanical, its possible theres corrosion there or even a Creepy Crawly or 2 residing in there.
    Last edited by gordon_s1942; 27-06-12 at 03:24 PM.
    I stand unequivicably behind everything I say , I just dont ever remember saying it !!

  • The Following User Says Thank You to gordon_s1942 For This Useful Post:

    dungbeetle46 (27-06-12)

  • #5
    Member dungbeetle46's Avatar
    Join Date
    Jun 2008
    Location
    South Aus
    Age
    60
    Posts
    320
    Thanks
    138
    Thanked 273 Times in 69 Posts
    Rep Power
    231
    Reputation
    1458

    Default

    I have been doing some more reading and it seems it should go out within 2 seconds and could be caused by a clogged inlet filter so will take a look there later today, if all else fails, I will take it to a specialist
    Thanks guys

  • #6
    Member dungbeetle46's Avatar
    Join Date
    Jun 2008
    Location
    South Aus
    Age
    60
    Posts
    320
    Thanks
    138
    Thanked 273 Times in 69 Posts
    Rep Power
    231
    Reputation
    1458

    Default

    just an update, I changed the microswitch, then pulled the guts of the thing apart and found a diaphragm that turns the gas on and off, this is operated from a plunger, this plunger was seized so I removed and cleaned and polished and reseated plunger and its working like a charm.
    Thanks all for your help

  • The Following 3 Users Say Thank You to dungbeetle46 For This Useful Post:

    Tiny (28-06-12),weirdo (28-06-12)

  • #7
    Premium Member

    Join Date
    Jan 2008
    Location
    Central Tablelands of NSW
    Age
    81
    Posts
    13,824
    Thanks
    1,242
    Thanked 3,806 Times in 2,525 Posts
    Rep Power
    1797
    Reputation
    56986

    Default

    Great result and thanks for the followup.
    I stand unequivicably behind everything I say , I just dont ever remember saying it !!

  • The Following User Says Thank You to gordon_s1942 For This Useful Post:

    dungbeetle46 (29-06-12)

  • #8
    Crazy Diamond
    Tiny's Avatar
    Join Date
    Dec 2010
    Location
    Tasmania
    Age
    64
    Posts
    6,391
    Thanks
    10,996
    Thanked 5,436 Times in 2,651 Posts
    Rep Power
    2156
    Reputation
    89057

    Default

    Quote Originally Posted by dungbeetle46 View Post
    just an update, I changed the microswitch, then pulled the guts of the thing apart and found a diaphragm that turns the gas on and off, this is operated from a plunger, this plunger was seized so I removed and cleaned and polished and reseated plunger and its working like a charm.
    Thanks all for your help

    AS I'M SURE YOU ARE A GAS FITTER BY TRADE, YOU WILL HAVE CHECKED FOR ANY LEAKS AFTER REASSEMBLY WITH SOAPY WATER.
    Cheers, Tiny
    "You can lead a person to knowledge, but you can't make them think? If you're not part of the solution, you're part of the problem.
    The information is out there; you just have to let it in."

  • The Following User Says Thank You to Tiny For This Useful Post:

    dungbeetle46 (29-06-12)

  • #9
    Banned
    watchdog's Avatar
    Join Date
    Jan 2008
    Posts
    2,966
    Thanks
    136
    Thanked 869 Times in 514 Posts
    Rep Power
    0
    Reputation
    8320

    Cool

    Quote Originally Posted by Tiny View Post
    AS I'M SURE YOU ARE A GAS FITTER BY TRADE, YOU WILL HAVE CHECKED FOR ANY LEAKS AFTER REASSEMBLY WITH SOAPY WATER.
    yeah - boats & gas , what an exciting combination

  • #10
    Premium Member

    Join Date
    Jan 2008
    Location
    Central Tablelands of NSW
    Age
    81
    Posts
    13,824
    Thanks
    1,242
    Thanked 3,806 Times in 2,525 Posts
    Rep Power
    1797
    Reputation
    56986

    Default

    You forgot Petrol fumes and sparking batteries when the ignition is turned on along with the 'Heavier than Air' LPG.....................
    I stand unequivicably behind everything I say , I just dont ever remember saying it !!

  • #11
    Member dungbeetle46's Avatar
    Join Date
    Jun 2008
    Location
    South Aus
    Age
    60
    Posts
    320
    Thanks
    138
    Thanked 273 Times in 69 Posts
    Rep Power
    231
    Reputation
    1458

    Default

    Quote Originally Posted by Tiny View Post
    AS I'M SURE YOU ARE A GAS FITTER BY TRADE, YOU WILL HAVE CHECKED FOR ANY LEAKS AFTER REASSEMBLY WITH SOAPY WATER.
    Yes checked everything with soapy water, no bubbles and I am a builder by trade and have installed many a gas hot water service, just never had to fix one and havent done one or used one for a long time.